Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Steam Main

Hello Everyone,
My question pertains to piping a steam main in this fashion. Has anyone piped a steam in this configuration below because of obstacles in the basement? If so has it been effective?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,848
    No problem. Happens routinely. The only comment I have is "automatic air valve"? Please. It's a main vent, and needs to be sized accordingly -- lots of discussions on here about how big. Also, they shouldn't be sited as shown, on a T at the drip, but about a foot or two back up the main from the drip, and on a nice nipple, not directly sitting on the main.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Hap_HazzardBigbri0104
  • AMservices
    AMservices Member Posts: 610
    The diagram your looking at is an example of how you would need to run a long parallel flow main.

    Say you have a building 400' long, with only 2' above "A" detention. By the time your main was at 240' you would have to drip the main and extend up to keep going
  • Danny Scully
    Danny Scully Member Posts: 1,440
    Yea I agree with @AMservices, that’s not really a method to avoid obstructions. If that’s what you’re looking to do there are a few ways to accomplish this. Attached is a picture of what @EzzyT and I did to avoid a chimney cleanout.
  • ethicalpaul
    ethicalpaul Member Posts: 6,660
    I wish the installers of my system had done that so I wouldn't have to hit my head on the main all the time

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Bigbri0104
    Bigbri0104 Member Posts: 28
    Thanks for the comments everyone. I will attach pictures from my basement to give a better visual.
  • Steamhead
    Steamhead Member Posts: 17,380
    It's called a "Rise and Drip".
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaul
  • Bigbri0104
    Bigbri0104 Member Posts: 28
    This message is in reference to Dan scully's picture of piping around and obstruction. The picture posted is a direct install from a specific page out of the "The lost art of steam heat."
    That specific install would require a wet return install on the lower end of the "U" shape pipe correct?
  • ethicalpaul
    ethicalpaul Member Posts: 6,660
    edited November 2019
    Nope, the condensate flows along the bottom route, filling it and continuing to flow after the Tee. The steam of course takes the high road. Neither is impeded and no wet return is needed.

    edit: I just noticed the cross piece in the lower right for cleaning out that bottom half, nice

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el