Weil-McLain EG Firing issue
Fast forward to a few weeks ago I installed another EG40 and upon firing I knew something wasn’t right, I checked my pressures then clocked the gas meter, same issue 90-95,000 BTU. Contacted supply house again and offered to give me a manifold and orfices off an older model boiler to see if the orfices were sized wrong.
So today I went back to do the first cleaning and figured I’d try and change that manifold. I pulled the new manifold off and compared the two, most obvious thing is there from different manufacturers one is black with a welded 1/2 pipe attaching to the manifold the older one is chrome with a coupling welded to the manifold to accept a standard 1/2” pipe nipple. Looking inside the two nipples told the whole story, the older one is fully opened 1/2” pipe size, the newer one had a blob of weld partially blocking the inlet to the manifold. The opening was approximately 1/4” hole.
Once I installed the older manifold and adjusted the gas valve the meter clocked perfect. Sucks I had to do all the trouble shooting on my dime, and now have to go back to another job to correct this issue. However this all still needs to be brought up to Weil-McLain, be now they have to try to figure how many boilers went out with that faulty manifold. I suppose most if not all the other contractors do not even test their equipment upon initialization. Unbelievable.
If anyone installed a Weil-McLain EG in the last six months I’d check it and clock the meter to be sure.
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
Comments
-
@Dave0176 I would try and get reimbursed from Weil Mclain2
-
-
I doubt it Ezz just wondering how many others are out there that don’t even know. We all know most grossly oversize their replacements so their getting benefited for this error lolEzzyT said:@Dave0176 I would try and get reimbursed from Weil Mclain
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
@Dave0176 , is the faulty manifold the black one with the nipple welded on or the chrome one with the coupling welded on?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Painted black one is the newer.Steamhead said:@Dave0176 , is the faulty manifold the black one with the nipple welded on or the chrome one with the coupling welded on?
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Dave,
Your making me nervous. We've installed many W/M EG boilers over the years not sure we've run into this problem yet. Thank you for sharing the information, may help a lot of us in the future.
I find it troubling that YOU have to to check the input of a natural draft residential boiler! Please tell me that you don't have to check the input on residential gas water heaters too...
I think W/M may do something for you. They are (at least used to be) a stand up company.0 -
> @Dave0176 said:
> (Quote)
> Painted black one is the newer.
That's interesting.
Have they changed before?
I swear my EG-45 manifold from 2011 was smooth black but the EG-40 replacement was rougher and just silver galvanized. I bought that a few years but don't remember exactly when. 2015 maybe? But who knows how long it was on a shelf.
Here's a picture of them.
The black one came with the boiler. The silver was bought from Supplyhouse.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Scott I don’t think you have to worry I’ve installed 100s of WM EGs over the years too, however these last few gave me trouble.ScottSecor said:Dave,
Your making me nervous. We've installed many W/M EG boilers over the years not sure we've run into this problem yet. Thank you for sharing the information, may help a lot of us in the future.
I find it troubling that YOU have to to check the input of a natural draft residential boiler! Please tell me that you don't have to check the input on residential gas water heaters too...
I think W/M may do something for you. They are (at least used to be) a stand up company.
As far as checking input we always do as part of the initialization process, which includes verifying gas pressures, clocking input, and a combustion analysis. The old adage is, if you ain’t testing your guessing.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Chris the newer style black ones are a bit different. I’ll take a pic tomorrow.ChrisJ said:> @Dave0176 said:
> (Quote)
> Painted black one is the newer.
That's interesting.
Have they changed before?
I swear my EG-45 manifold from 2011 was smooth black but the EG-40 replacement was rougher and just silver galvanized. I bought that a few years but don't remember exactly when. 2015 maybe? But who knows how long it was on a shelf.
Here's a picture of them.
The black one came with the boiler. The silver was bought from Supplyhouse.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Here’s the boiler with the older styled chrome manifold installed.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Did you check the size of the orfices of both manifolds to see if there was a different size orfice supplied. Many years ago, a boiler of that design, and I can't remember the mfg name, utilized a manifold pressure of 4" instead of the normal 3.5". I argued with their engineering department until the conversation got nasty. They told me to "go away" and hung up the phone.0
-
> @ChrisJ said:
> > @Dave0176 said:
> > (Quote)
> > Painted black one is the newer.
>
> That's interesting.
> Have they changed before?
>
> I swear my EG-45 manifold from 2011 was smooth black but the EG-40 replacement was rougher and just silver galvanized. I bought that a few years but don't remember exactly when. 2015 maybe? But who knows how long it was on a shelf.
>
> Here's a picture of them.
>
> The black one came with the boiler. The silver was bought from Supplyhouse.
>
One has 5 burner bungs, one has 4. For the same boiler?0 -
> @HVACNUT said:
> > @ChrisJ said:
> > > @Dave0176 said:
> > > (Quote)
> > > Painted black one is the newer.
> >
> > That's interesting.
> > Have they changed before?
> >
> > I swear my EG-45 manifold from 2011 was smooth black but the EG-40 replacement was rougher and just silver galvanized. I bought that a few years but don't remember exactly when. 2015 maybe? But who knows how long it was on a shelf.
> >
> > Here's a picture of them.
> >
> > The black one came with the boiler. The silver was bought from Supplyhouse.
> >
>
> One has 5 burner bungs, one has 4. For the same boiler?
Read what I typed my friend.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
> @ChrisJ said:
> > @HVACNUT said:
> > > @ChrisJ said:
> > > > @Dave0176 said:
> > > > (Quote)
> > > > Painted black one is the newer.
> > >
> > > That's interesting.
> > > Have they changed before?
> > >
> > > I swear my EG-45 manifold from 2011 was smooth black but the EG-40 replacement was rougher and just silver galvanized. I bought that a few years but don't remember exactly when. 2015 maybe? But who knows how long it was on a shelf.
> > >
> > > Here's a picture of them.
> > >
> > > The black one came with the boiler. The silver was bought from Supplyhouse.
> > >
> >
> > One has 5 burner bungs, one has 4. For the same boiler?
>
> Read what I typed my friend.
Cut me some slack. EG-45, EG-40, 2015, I think. Elf on a shelf? I'm still on my first cup.0 -
Same orfice 2.45mm opening.retiredguy said:Did you check the size of the orfices of both manifolds to see if there was a different size orfice supplied. Many years ago, a boiler of that design, and I can't remember the mfg name, utilized a manifold pressure of 4" instead of the normal 3.5". I argued with their engineering department until the conversation got nasty. They told me to "go away" and hung up the phone.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
> @HVACNUT said:
> > @ChrisJ said:
> > > @HVACNUT said:
> > > > @ChrisJ said:
> > > > > @Dave0176 said:
> > > > > (Quote)
> > > > > Painted black one is the newer.
> > > >
> > > > That's interesting.
> > > > Have they changed before?
> > > >
> > > > I swear my EG-45 manifold from 2011 was smooth black but the EG-40 replacement was rougher and just silver galvanized. I bought that a few years but don't remember exactly when. 2015 maybe? But who knows how long it was on a shelf.
> > > >
> > > > Here's a picture of them.
> > > >
> > > > The black one came with the boiler. The silver was bought from Supplyhouse.
> > > >
> > >
> > > One has 5 burner bungs, one has 4. For the same boiler?
> >
> > Read what I typed my friend.
>
> Cut me some slack. EG-45, EG-40, 2015, I think. Elf on a shelf? I'm still on my first cup.
I converted my EG-45 to an EG-40. The only difference is 1 less tube and the draft hood. If course the spacing is different between tubes etc.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
how does that work? dropping 5 to 4 tubes?
don't the burner tubes line up with cast sections?known to beat dead horses0 -
> @neilc said:
> how does that work? dropping 5 to 4 tubes?
> don't the burner tubes line up with cast sections?
From 6 to 5 and no they do not.
They sit under it like a pot on a stoveSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements