Btu's in hand, how to size radiator?
mikemac52
mikemac52 Member Posts: 58
I have my coolcalc manual J in hand and the Btu requirements per room. How close to come to the btu numbers required with the capacity of the radiators? Should I leave any headroom? The cast iron radiators were quite large and will be downsizing some of them for space saving reasons. (I mean, the wife told me to...)
  • JohnNY
    JohnNY Member Posts: 3,398
    Size them to the heat loss of the room within 5%.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Jamie Hall Member Posts: 27,630
    And, since this is tagged under hydronic, not steam, be sure to account for the temperature you plan for your circulating water.
  • Zman
    Zman Member Posts: 7,614
    If you are only downsizing some of the cast iron radiators, be careful of your zoning. If you have existing radiators which are 200% of design with new that are 105% of design, you would be wise to zone them separately or add TRV's
    Albert Einstein
  • mikemac52
    Thanks for the quick replys! Hoping to keep the water at 140 F. Would have been 130 F but for a bad interior design Choice...