Steam Boiler 0-3 PSI Gauge Install
Comments
-
1. 45 minutes running a totally cold system might likely not produce any pressure
2. Was the valve closed the whole time?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
@ethicalpaul Yes I did open the valve for a few minutes to see if any pressure registered.Crown Boiler Bermuda Series model: BSI103, BTU output: 85,000, single pipe steam system1
-
The installation of the gauge and pressure control looks great . However, I prefer to have the gauges and pressure controls being mounted as far above the water line as possible to insure that the piping has less chance of getting plugged. This comes from being mostly into high pressure industrial steam.2
-
Many systems run under an ounce or two of pressure (<0.125 psi) before the radiator vents start closing. That likely won't register on a 3psi gauge.
You might be in the low pressure club. If you want to know what pressure you're operating at, go to a lower pressure gauge.
Also, I would leave the valve open for the whole test. The pigtail should protect the gauge.Burnham IN5PVNI Boiler, Single Pipe with 290 EDR
18 Ounce per Square Inch Gauge
Time Delay Relay in Series with Thermostat
Operating Pressure 0.3-0.5 Ounce per Square Inch2 -
Are the radiators/returns getting hot?
Have you clocked your gas input?
Is your boiler undersized..?
Ultimately if the system heats (with a load on it), and you don't get pressure reading, you may want a gauge that reads in inches and ounces, and put a vaporstat (eg: L408J1009 Honeywell) on the boiler for your operating pressure control.
Aside: hoping everyone is using a digital (eg: Hydrolevel VXT with bypass piping and shut off valves) feeder on your steam boilers
PS: To my understanding only brass control trim may be used on steam boilers everywhere. Eg, all control nipples 1/4" - 1/2" (beyond factory installed at tappings), tees, pigtails, etc control/gauge train shall have clean outs. Technically that steel pigtail should be brass.
1 -
@bill_kitsch69, yes the radiators and returns did get hot and my boiler is slightly undersized. I did not clock any gas input. What do you recommend for that? I do not use any auto feeders, my boiler is manual feed only. When you say that the steel pigtail I have should be brass, is there a specific reason for that? Thank you for your help.Crown Boiler Bermuda Series model: BSI103, BTU output: 85,000, single pipe steam system0
-
Thank you everyone so far for your input.Crown Boiler Bermuda Series model: BSI103, BTU output: 85,000, single pipe steam system0
-
He suggested clocking the gas meter to ensure you are getting approximately the expected amount of fuel burned so you see if the boiler is putting the expected amount of heat into your house (in BTU). Like if half of your burners were clogged up, or if someone had cranked down the gas pressure on your boiler that would be bad and you could tell because the fuel use rate would be way less than expected.
Check google, or here is a thread about it: https://forum.heatinghelp.com/discussion/65095/clocking-a-boiler
The brass pigtail is said to better resist clogging (and certainly rusting). They can clog up amazingly fast depending on water conditions. Lots in the field are steel though, including mine before I replaced it.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
@BrianT1077BrianT1077 said:Hello everyone! Tonight I installed a 0-3 PSI gauge on my boiler. Check out the install pictures and let me know of any concerns or ideas. Also I ran the boiler tonight for about 45 min and got no reading on the gauge. What do you think? Thank you everyone for your input!
FYI - Currently, Grainger has a clearance on a center mount, 0 to15 oz. low pressure gauge - at a super low clearance price. I just bought one.
See "GRAINGER APPROVED 2-1/2" Low Pressure Pressure Gauge, 0 to 15 oz./sq. in."Weil-McLain EG55 2 pipe Vapor System
OP Pressure .10 -.25 oz
8-Way Boiler Water Treatment
Barnes & Jones Big Mouth Vents1 -
@EdwinD, thank you for the info, I will check it out.Crown Boiler Bermuda Series model: BSI103, BTU output: 85,000, single pipe steam system0
-
I found this thread when search for a low pressure gauge for my steam boiler. I would like to have a similar set up. After reading your post, I'm thinking maybe I should get a gauge that only goes up to 1 psi.
Also, wouldn't the gauges both be better protected from the steam if you used a tee above the pigtail and then installed the gauges?
Any thoughts?
Thanks,
JB1 -
Not necessarily. One is manufactured with an integral internal siphon.JohnBeemer said:I found this thread when search for a low pressure gauge for my steam boiler. I would like to have a similar set up. After reading your post, I'm thinking maybe I should get a gauge that only goes up to 1 psi.
Also, wouldn't the gauges both be better protected from the steam if you used a tee above the pigtail and then installed the gauges?
Any thoughts?
Thanks,
JBContact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
Ok, The 0-30 on the boiler shows nothing so I'm thinking about getting a gauge that measures 0-30 wc which is about 1 psi.
Thanks for the info,
JB0 -
> no reading on the gauge
If the "house" (all radiating surface) is "bigger" than the boiler or the BTU demand, you won't get gauge pressure. Steam can rise with really insignificant pressure loss, if it condenses in the radiators real fast.
I had this in a house where one owner apparently added several radiators to an already over-raditatored system, and the next owner converted to a Right-BTU (for the house) oil boiler. In cold weather it would steam freely, the oversize radiators got hot at one end and cold at the other. Pressure never happened. House got warm perfectly well. It was just more radiator area than the house needed. It could have heated fine with half the cast-iron installed.
In COLD windy weather the needle just budged, so I knew it wan't stuck.
I don't see a need to know exactly how low the pressure is, as long as there's good heat in the radiators. The pressure gauge is there to tell you about dangerous HIGH pressure. Installing a 1psi gauge seems dubious in case you ever do need 5psi on a super-cold day- the gauge could burst.
Also remember "vacuum" systems. While they could build pressure, they were intended to be leak-tight so you could recover steam heat even as the boiler cooled to 170 degrees, saved coal, might heat through the night without stoking.0 -
I'd go with a 0 to 3 or 0 to 5 gauge. You need to keep the 0 to 30 as well to keep the insurance company and building inspectors happy.
You don't state whether your system is one pipe, normal two pipe, or vapour; all three will be fine with a 0 to 3, assuming the pressuretrol or vapourstat is set correctly -- and working.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Not sure what you mean if the system is 1 or 2 pipes.
There's only 1 pipe going to each radiator.
Thanks,
jb0 -
Then it's what is called a one pipe system, and each radiator has it's own vent. They generally run best at pressures not over 1.5 psi.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
FYI: That pressure gauge looks like a cheap one they are selling on Amazon. I found the calibration out of the box to be off, about 0.2+ PSI lower than the more expensive Winters gauge I got from SupplyHouse. (Which isn't a high precision gauge either.) I wouldn't be surprised if others are ever further off new in box. So it's possible the system is generating some pressure but the gauge isn't showing it because it's calibrated too low.
It's easy to adjust the calibration screw on the Amazon gauge to at least get it closer to reality.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements