Steam leak

Snowmelt
Snowmelt Member Posts: 1,425
I been doing some work on a steam system, it finally failed at end of season, now they called me to replace it.
The big problem besides not piped correctly is that it was using a lot of water but there was no physical leak. All the returns are visible to the eye. There are no puddle of water anywhere. It’s a rather long as in linnier feet of piping, no water on the ground anywhere, the three leaks that we did find did have water on the ground.
There are roughly 6 - 8 steam traps and one condensation pump.
Can I use a smoke test to try to find a leak?
Can I use air if I cap the vents?
What other alternative would you like to see done?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    The most common place for a steam system to leak is the boiler, unfortunately. Since you are replacing the boiler, that should take care of that one.

    The next most common is tired wet returns. The best way to check those is to rig something up so that you can fill them with water -- just the open end of the connection up to the Hartford loop will do nicely -- and fill them. If the water drops... then you have some detective work to do to find the villain (were I doing it, and had three known leaks, I'd probably replace all the wet return piping -- but that's me).

    Then after that... steam mains, runouts, and dry returns very rarely leak. Fitting do, now and then. Valves do, rather more often -- and steam vents on radiators often do. You could use air, but you'd have to plug all the steam vents, which is a pain -- and anyway that would tell you you have a leak, but not where.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • neilc
    neilc Member Posts: 2,854
    with the boiler turned off,
    flood the boiler to header height and check under boiler,
    flood to mains and vents height in basement and check some more,
    vents can leak steam = water
    valve stems at rads can leak steak = water
    known to beat dead horses
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,477
    If the piping is not leaking for sure then the most likely reason for water loss is the steam traps. The traps blow steam which comes out the vent on the condensate pump never to be seen unless your there when the boiler is running
  • neilc
    neilc Member Posts: 2,854
    condensate pump,
    I missed that,
    careful with my flood testing, you may make a mess,
    what ed says above also
    known to beat dead horses
  • John Ruhnke
    John Ruhnke Member Posts: 939
    A leaky steam vent is easy to find. Its noisy and steam bellows from it. Check around the house while the system is running to find any leaky vents. They may not show up as water on the ground.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • JUGHNE
    JUGHNE Member Posts: 11,276
    edited September 2019
    While redoing some dry return piping on older systems with multiple return pipes, I installed a tee with 24-30" riser pipe on each dry return as soon as it entered the boiler room.
    This indicator will allow you to see which section of the building has leaking steam traps and keep that steam out of the cond return pump. From 12' below an inexpensive ($350) FLIR will show the steam fog cloud even if you can not see it with your own eyes.
  • Snowmelt
    Snowmelt Member Posts: 1,425
    I replaced all steam vents at end of last season.
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Valve stem leaks can be invisible but add up.
  • acwagner
    acwagner Member Posts: 512
    Are the pipes insulated? How much of the piping isn't accessible?
    Burnham IN5PVNI Boiler, Single Pipe with 290 EDR
    18 Ounce per Square Inch Gauge
    Time Delay Relay in Series with Thermostat
    Operating Pressure 0.3-0.5 Ounce per Square Inch

  • Snowmelt
    Snowmelt Member Posts: 1,425
    No pipe is insulated, all the pipes are above ground some are in walls but 90% is available
  • acwagner
    acwagner Member Posts: 512
    You could try using compressed air and soapy water since most of the system is accessible and the pipes are visible. It'll take some time to do.

    I assume this is single pipe system.

    If so, remove the radiator vents and main vents and plug them. Also remove the pressuretrol, and drain the boiler. Put a compressed air fitting somewhere on the system, and put 2-3 pounds of pressure in the system. Then use soapy water on all the pipe fittings and radiator joints.

    As others have mentioned, the leaks are most likely at unions and valves. If you have a pin hole leak in a pipe, that might be harder to find. You might luck out and hear the air escaping in that case if the space is quiet enough.

    My guess is it's several small leaks vs. a single big one.

    I did this on my system and I was able to tighten it up. Most of my leaks were at the radiator valves (stems and unions).
    Burnham IN5PVNI Boiler, Single Pipe with 290 EDR
    18 Ounce per Square Inch Gauge
    Time Delay Relay in Series with Thermostat
    Operating Pressure 0.3-0.5 Ounce per Square Inch