Big house, minuscule boiler room.

This is a boiler replacement job, but it reminds me of how we have to fight with the AIA to get a decent amount of space for our equipment.

I've learned to ask for twice the amount of space than I need and take the flak later.


8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • Ironman
    Ironman Member Posts: 7,556
    You're a better man than I am. Why no indirect?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Solid_Fuel_Man
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Wow! I’d call that a 'mechanical nook'. Nice job!

    Are they going to be able to replace the water heater in the future without taking down a wall?? Of

    There was an error rendering this rich post.

  • I have more and more customers that are cautious about their DHW. If their boiler packs up, they at least want their hot showers and I'm not about to argue with them.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    Rich_49
  • ChrisJ
    ChrisJ Member Posts: 16,317

    I have more and more customers that are cautious about their DHW. If their boiler packs up, they at least want their hot showers and I'm not about to argue with them.

    This was a big reason I didn't do it.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    SeanBeans
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    Retired and loving it.
  • Lance
    Lance Member Posts: 305
    Just because empty space doesn't contain anything is not a reason to eliminate it. Space is the first priority in every successful design, unless you are never going back, or will not be responsible for lacking it. Kudos to us who can do without space but we really shouldn't let designers steal the space required for service.
  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,217
    edited August 2019
    Lance said:

    Just because empty space doesn't contain anything is not a reason to eliminate it. Space is the first priority in every successful design, unless you are never going back, or will not be responsible for lacking it. Kudos to us who can do without space but we really shouldn't let designers steal the space required for service.

    I consider myself lucky if they ask how much room we need. Most of the time, they say, "There's your boiler room.".
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    Solid_Fuel_ManCanucker
  • Henry
    Henry Member Posts: 998
    That type of installation does not meet our clearance required in our CSA B149.1code! The gas utility or AHJ would tag it.
  • HotanCool
    HotanCool Member Posts: 55
    I'm glad I live and work where we have Basements! :)