Buderus GB142 ... multiple corrosion issues.
A noob here, thanks for all the terrific advice. Hoping to get your views on the following. Pics attached.
I've got a new-to-me, approximately 10 year old, natural gas fired GB142 w/ indirect Buderus HW tank. 3500 sq ft house with cast base boards and radiators. The issues ...
- the pump manifold is rotting away. Why? Particularly concerned with the related corrosion within the boiler. I read the manifold is a problematic original, and there was a replacement offered at some point?
- the vent piping seems to be discolored, and the 90 degree elbow just before the turn to go outside the house appears to be leaking. Condensate not draining correctly and caused failure of the PVC cement joint? Seems a slope issue with the exhaust line? Exhaust too hot?
- can't see it in the photos, but their is a hole (1" round ) rotted through the back of the (aluminum?) exhaust vent adapter (no worries, the unit is shut off). It was leaking exhaust directly into the basement! I assume this was a condensate issue. New flue vent adapter kit (plastic) has arrived and is ready to go in.
HX has not yet been disassembled. No idea how often it was cleaned. Probably due for cleaning.
So I'm going through the math repair versus replace. Also need recommendation for good Buderus service tech in Eastern MA.
Much appreciate your opinions on of all this.
Cheers
  • Ironman
    Ironman Posts: 7,982
    I'd say a severe lack of maintenance. No excuse, that's the easiest mod/con to clean.
    Just go through and clean or replace whatever needs it.
    Is there an AM10 boiler reset control? The flue pipe deterioration leads me to believe not. Without it, the high limit on the boiler is 194* which is unnecessary and inefficient.
    Bob Boan
    hot_rod Posts: 28,856
    Check your model number, see if any recalls are open.
    https://www.cpsc.gov/Recalls/2010/Bosch-Thermotechnology-Recalls-Boiler-Survey-Kits-Due-to-Fire-Hazard/
    Water quality is critical in aluminum block boilers, a tight ph, below 7 gpg hardness, and chloride level below 100 for the fill water.
    Some installer like to add corrosion inhibitors to protect the HX. Conditioners buffer the ph, introduce oxygen scavengers, and add film providers to protect all the metals. Conditioners do need maintenance and occasional buffers added.
    Here are water specs, and approved aluminum friendly conditioners for one of the newer models.
    If you have a manual check it for cleaning and service info,
    if not, download the manual for your exact model.
  • GW
    GW Posts: 5,299
    Seems like you may have anti freeze in the system.
    That pipe is showing corrosion in an odd spot, is there something dripping on it?
    The manifolds have been a pain at times:
    The “flue adapter” has also been a problem. We do a couple a year, 1/d day project
    when we get new customers calling us for GB142 service, we have them read our GB142 letter and acknowledge it. It’s filled with items that can come back and haunt us
    If it has antifreeze and it hasn’t been serviced in a while, start saving for a new boiler.
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • woobagooba
    woobagooba Posts: 186
    edited August 2019
    @Ironman ... yes an AM10 is installed and I see the the outside temp sensor mounted a few feet below the exhaust.
    @ Hotrod. I did locate the Buderus water chemistry guidelines. I will check with the town (I am on muni water), or better yet do a Rhomar test. And also will check on that recall notice.
    @ GW. Unlikely there is antifreeze in system ... I will check.
    PO claims unit was serviced annually in Fall. Service tag indicates it was serviced Fall 17 and 18. I popped open the HX burner fan and condensate collector plate. I ask you, is this one heating season of scale buildup?
  • woobagooba
    edited August 2019
    Just noticed corrosion in the condenser plate corners? Cause of the corrosive leak on the supply and return lines to the lower right inside the enclosure?
  • Ironman
    edited August 2019
    Clean the heat exchanger by spraying mineral oil on it, then turn it on. Avoid getting it on the ignitor and flame rod. Repeat if needed (very likely).
    Get a new gasket for the collector plate and maybe a new trap. Clean they flame rod with a dollar bill or replace it.
    As, mentioned: it's suffering from a severe lack of maintenance. The previous owner may have paid someone to maintain it, but they grossly failed to do so.
    Bob Boan
    CanuckerRich_49
  • Zman
    Zman Posts: 7,614
    A few quick thoughts:
    The vent piping in the picture has some issues. One of the pipes is definitely cellular core, confirm that the exhaust pipe is not.
    The vent pipe does not appear to be sloped correctly back to the boiler. Zip ties off of domestic piping is not a proper support. If the vent pipe is yellowed from excessive heat, it needs to be replaced.
    The HX with that level of fouling is and indication of neglect. I would also wager that a combustion analysis has never been performed.
    The water chemistry is critical with that boiler. What are the levels now and what impact has that had on the internals.
    When you consider what it will take to get this boiler back in operation (for a little while before something else goes bad), how does that compare to the cost of installing a new boiler?
    In my experience, 10 years life expectancy is about average for that model boiler (local water quality and maintenance play a huge factor). I would sawzall it out and get a new stainless steel firetube boiler.
    Albert Einstein
  • woobagooba
    Thank you. Re: the water quality. I intend to have Rhomar do a test. From what point in the system should I extract the sample? The make-up water supply is from the muni water feed.
  • Zman
    Zman Posts: 7,614
    It would be interesting to know what the existing water in your system is like. You should be able to get that from a boiler or purge drain. I would dump the first bit that may contain sediment in order to get a good representative test.
    I would also test the tap water you intend to refill with.
    You can probably get an idea about the tap water chemistry from the water departments website.
    Albert Einstein
    edited August 2019
    Decent video about cleaning the HX:
    https://www.youtube.com/watch?v=fZTu37sEELg&list=PLq4NGiyqj85YbH1rMZ1lfRFwEj4kkmFxb&index=5&t=0s
    These are the parts I require my GB142 customers have on hand:
    HSI igniter 7099006
    ionization electrode 78195
    Cover hinges 7099834
    For Buderus indirects:
    replacement anode rod 7185715690
    manhole cover gasket 87185725380
    All available at supplyhouse.com
    ZmanNoelRich_49
  • vilord
    vilord Posts: 50
    edited August 2019
    I have a GB142/24 in my home, and it needs maintenance, including water quality analysis... I was very unimpressed by the last company I had come out to service it (they charged *$600* for annual service?! And they didn't test the water or fix the leaks. that's a quarter the cost of a complete replacement 142...), so I am also curious if there's a good Buderus tech in the area (I'm in metrowest).
    The corrosion on the manifold looks like mine... the combination plastic/rubber fitting between the manifold and the exchanger (where the pipes go through the plastic housing at the bottom of the boiler) are known issues, and mine has had an occasional drip leak as long as I've owned it, which gets worse if the boiler is shut down for a few days.
    I watch craigslist for GB142's and have considered buying one just to have a replacement for when the aluminum HX corrodes through. Mine was installed in 2012, so I figure I've got maybe 3 years before it is junk.
  • woobagooba
    Thanks all ... and an update.
    I was able to engage local Buderus support providers and contacted several GB142 owners. Service tech told me the amount of buildup in the HX was normal for a New England heating season, and the service tag record, the original owner, and collection of replaced parts do confirm the unit was serviced last few years. But IMO the minimum was done. It was likely cleaned, but clearly the decaying manifold was not remedied.
    More than one person has told me they have had HX warranty replacement at about year 8, parts and expertise are hard to obtain, etc. I'm on year 11 with a questionable manifold, rotted flue adapter, gaskets needed, indirect tank is not looking good, etc.
    To bring this GB142 up to par will cost several kilo-bucks. I'm working on a heat load calc and pricing out replacement units ... both combi and indirect hw. Trying to go with stainless fire tube.
  • The Rhomar report ... this for the make up water (the system will likely be flushed and refilled as part of reno)
  • Quick update as winter approaches.
    The plan is to nurse this unit through this winter (of premises renovation).
    Flue adapter, condenser plate gasket, and blower fan required replacement. Pitch of the intake and exhaust was corrected.
    Cleaning procedure was performed.
    Unit does fire, but exhaust exited the condensate trap as I neglected to re-fill the exhaust pipe trap (above the boiler) ... remedy that tomorrow.
    The S100 indirect tank is shot.
    Next week I bring in a pro for annual checkup.
    Its been be an education on this mod-con. I'm in a much better position re: decision making for its replacement (likely an IBC, Lochinvar, or Veissman).
    Funny story. One of the local Buderus listed retailer provided a replacement quote ... offering a GB142! Please no!
  • GW
    GW Posts: 5,299
    Very good boiler, for its day. In 2005 it was that of the high priced Viessmann WB1B. Back then the Viessmann’s were huge dollars. Anyway, many people never got the memo that the GB142 needed maintenance, so “poof”, they started acting up and falling apart
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • I am having many of the above corrosion issues. Boston Suburb. Lousy Town Water. What would you recommend as replacements to a pair of GB142/45s? Supplying both heat and hot water.
  • vilord
    vilord Posts: 50
    I think when mine goes (also Boston Suburb), I will be looking at either the Bosch Greenstar or the Veissmann Vitodens... Both talk about having a stainless steel HX.
    But more important will probably be the recommendation from whichever installer/servicer I end up going with... these things are complicated enough that I want one where the local techs actually know what's up.
    Couple years back I called 4 difference service companies, none of them knew the proper procedure for annual service on my GB142 (and none of them were going to look at the manual either), so I want something that's more... erm... standard.
  • kcopp
    kcopp Posts: 4,744
    @vilord Bosch Greenstar is not a SS heat exchanger.
  • vilord
    vilord Posts: 50
    oops. guess i was looking at the spec on the combi, which i won't need. okay, greenstar is out!
  • Other than Bosch or Veissmann, is there a third Stainless Steel option. Reliable, easier to service?
  • Zman
    Zman Posts: 7,614
    I prefer the stainless firetube HX many brands are using. They have decent mass, very little flow resistance and will never foul up like that POS.
    Lochinvar WHN is prefered in my area. Triangle Tube, Burnham, HTP and several other manufactures make a comparable unit.
    Albert Einstein
    vilord
    Installers should be closely watching water quality, or you should :)
    I'd guess if you are in an area where it snows, your chloride levels from public or private water sources are high. That would need to be addressed in the fill water.
    Aluminum, stainless, you have no warranty out of the box if the fill water doesn't meet the manufacturers spec.
    Brand is not always the reason boilers fail.
    65 brands of mod cons on the market, look for brands that are common and supported in your area. Lochinvar, NTI, HTP, IBC, US Boiler, Utica, are just a few of the well know brands. They all have stainless modcon options
  • vilord
    vilord Posts: 50
    How do you address that in the fill water? Some sort of mixer tank of antifreeze/treatment that gets pulled in?
    My GB142's HX hasn't failed yet, but no servicer or installer even talked about testing the water, and since the stupid galvanic isolating couplings drip-drip-drip, i'm sure any additives in the water have been quite diluted.
    With any boiler installation or replacement it is wise to know what fluid will be used. I would certainly run a cleaner through a new boiler installation to take installation and manufacturing residue out, solder flux, pipe dope, assembly lubes and glues, etc. Then use a good fill water.
    The fill water needs to meet several critical numbers, as outlined in the installation manual. Ph, hardness and TDS, some go into more details.
    Ph , hardness and TDS can all be tested on the jobsite with a few inexpensive tools or meters. I use a small pocket electronic Ph tester, confirm accuracy yearly with test fluid.
    A dropper type hardness kit, Hach for example, and a stick type TDS meter. Find all these at pool suppliers or online.
    You can find folks to test water locally or send a sample to most any of the hydronic chemical providers for a test. Some wholesalers will test water also.
    Lastly I add a hydronic conditioner, especially with Al boilers. Some brands send a container of conditioner for you to add.
    But don't put the conditioner into a dirty or bad water system, it will not help you much.
    Yearly or every two years sample the water. If you use hydronic conditioners you need to get a test kit from the chemical manufacturer that tells the condition of the fluid. or send a sample to the conditioner manufacturer. It is no longer plain water and needs a specific test to check the condition of the inhibitor. Occasionally it may need an inhibitor boost..