Mitsubishi Split Refrigerant Line Sweating Water?
Is it possible the refrigerant line is the cause of the leak? If it is, what is the best fix? Is this the right kind of insulation for the piping and if now what should be used?
Thanks for your help.
Comments
-
Think I just answered my question on the refrigerant line. I have another in my attic on the east side of my home and this one as you can see is slightly leaking through where it’s zipped tied in one location.
What is the best way to fix this? Is this the wrong insulation for an uconditioned space and if it is, what should be used? Also these lines clearly should not be zip tied...how should they be connected?0 -
Both lines on a mini split are going to be below the dew point during cooling operation (means they're going to be cold & sweating). They must be insulated, with no gaps in the insulation, for the entire length.
Zip ties on any lineset insulation are a mark of non-professionalism, for the obvious reason seen in the picture—they compress the insulation & can even rip it if pulled too tight.
The quickest fix would be to wrap several layers of foam insulating tape around the zip ties, along with any gaps or holes in the insulation. If I absolutely have to tie something on to a lineset, I use this, being sure to cut the tape into pieces so that it can be easily applied without stretching it.
Runs through non-conditioned spaces may require more insulation than is provided from a standard mini split lineset. As long as both lines are individually insulated, some of this around both lines would probably work adequately.
The fact that you've got damage to your house should get the installer out there pretty quickly to fix the problem.
1 -
Usually the insulation is supplied covering both copper tubes as a line set.
If insulated on site then 6' lengths are slipped over the copper lines and the butt joints would be taped.
Both lines must be insulated with no gaps or openings that will cause the attic humidity to condensate on the cold lines and drip.0 -
Thanks to both of you on the response. Believe they used the insulation that same with the pipes. What type insulation should be used if I’m in an area where the attic can get well above 100 degrees in the summer and below freezing in the winter?
Assuming any insulation on the exterior of my home should be replaced too? Believe they would have used these pipes which had 1/2” insulation on it:
https://www.ecomfort.com/manuals/line_sets_brochure.pdf0 -
½" Armaflex insulation is more than adequate. If you're concerned about it passing through an unheated space, more insulation could be added. Like I mentioned before, you could add additional insulation around the lineset as a whole.
If water is dripping/leaking from the lineset, it's a gap in the insulation that's causing it. Warm moist air is coming in contact with the cold pipes & condensing water, exactly like what happens in the evaporator (inside part). The water is running down the lines to a low point & dripping out. The holes in the insulation must be located & repaired.
0 -
Thanks. If they use an insulation tape over all the spots where it ripped (basically every one to two feet where the lines were either clamped or zip tied for all 8 units) this will hold up over time? The adhesion won’t deteriorate from the heat and humidity in summer and cold in winter?0
-
If the Armafles is clean when the tape is applied, it should stay stuck. It should be repaired any place you can see copper or reasonably think copper may be exposed to the air. Gouges that don't penetrate the Armaflex should be ok.
To get enough water to damage the drywall like that indicates a rather large condensate leak (large gap in the insulation), most small tears won't produce that much water. How sure are you that the condensate drain itself (pr possibly a different one) doesn't run along that lineset?
0 -
I’m positive on the drain line. There are none in my attic. This units drain line goes straight outside and down a line hide. All other lines go through the attic before going down to the condenser it’s connected to in the other side of my house.
It has been 100+ degrees here since Friday and really humid for days before. The line that caused this damaged is also in the west facing space of my attic and unconditioned so has to be the hottest place in my house. When we first checked the line yesterday morning it was not leaking but by the afternoon it was. Guess it must have been leaking all summer and this was the cumulative result from the hot humid weather we have been getting?0 -
Wrap with armaflex tape. You could use some duct tape (they make Black duct tape) where the armaflex tape ends to secure it from unwrapping0
-
Thanks. And this will hold up indefinitely? I ask as I had a separate issue where they duck taped the drain line to the main one and it fell off. This was sitting in a line hide on the exterior of my home, but it also happened only 9 months after installed.0
-
If it’s ripped that bad and water logged replace it.0
-
Guy there now. Said he found about a 3 inch section with exposed copper pipe which was above where the damage to ceiling occurred. Said he wrapped it with armaflex along with a tape on top of it. Also for that line he removed all zip ties and clamps and did the same thing.0
-
Sounds like they found the problem.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements