Heating below the water line
McSteamer22
Member Posts: 23
Hey team,
I’m looking to put a radiator below the water line. I know there’s a way just forget the specifics. Any diagrams would be awesome. I read over lost art but didn’t find anything. Also not sure if it’s specific to 1 or 2 pipe systems
Thanks in advance
I’m looking to put a radiator below the water line. I know there’s a way just forget the specifics. Any diagrams would be awesome. I read over lost art but didn’t find anything. Also not sure if it’s specific to 1 or 2 pipe systems
Thanks in advance
0
Comments
-
Either one pipe or two pipe. If the whole show is below the water line, it's dead easy -- provided you can get at least one opening into the boiler below, but not too far below, the water line There's usually a tap which will work. Pipe into that, go down to the floor, put on a small circulator -- won't need much -- run over to your radiator, take the radiator outlet and run back to some useful spot like a wet return.
Done
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Hey Jamie, I didn’t even think about doing it hydronicly,
I thought there was a way using the steam, some configuration of a check valve and f and t trap0 -
Below the boiler water line, it needs to be a hot water loop.0
-
Actually, there is. It's a lot more complicated. It requires a certain minimum steam pressure. It requires a check valve and an F&T. And it's a pain in the neck. Do it the easy way. Besides, you can control the circulator with it's own thermostat -- giving you control of just that zone.McSteamer22 said:Hey Jamie, I didn’t even think about doing it hydronicly,
I thought there was a way using the steam, some configuration of a check valve and f and t trapBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Or it could be done using a condensate pump. But as @Fred & @Jamie Hall pointed out hydronic is the way to go.
The book you need is "How Come" a @DanHolohan0 -
Jamie Jamie Jamie, no style points or creativity for just slapping in an ole circulator.
We are masters at manipulating the vapor,
I don’t have a specific application but I want to learn.
I’ll take any crumbs you have on the matter,
I have the lost art revisited (bible) and it doesn’t mention.
From one nutmegger to another
Thanks0 -
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
-
For one pipe steam you can take the end of the steam main ( dry return) and drop down below the water line, run into your radiator and then out the radiator and continue running below the water line to the boiler return. It will probably work better if you supply the radiator at the top and the return from the bottom. Both bottom tappings together should work too. Both top tappings probably won't work as the hot water will travel across the top of the radiator and not fully heat the radiator. You'll want a large steam main if you can so you'll get more condensate flow. We've done some this way and they work quite nicely. This probably would be an effective way to use a condensing steam boiler with one pipe steam, since the condensate will return quite cool. As an alternative, just install a piece of fin tube in place of the return line and provide some sort of housing to create convective air currents.To learn more about this professional, click here to visit their ad in Find A Contractor.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements