Split Flue
Dan Foley
Member Posts: 1,260
I looked at this one today. It was a survey and estimate to replace a steam boiler in Silver Spring, MD. This is on a 2-pipe system. The home was built in 1928.
I have never seen a flue pipe split and vent up two separate chimneys. The home inspector red tagged it. Is this a code violation? I could not find anything in IMC or NFGC but maybe I missed it?
I have never seen a flue pipe split and vent up two separate chimneys. The home inspector red tagged it. Is this a code violation? I could not find anything in IMC or NFGC but maybe I missed it?
0
Comments
-
-
It must have been easier than chopping into the masonry.
Looks like a lot of boiler, perhaps replacement will be smaller.
Is this a 2 pipe counter flow system?
I have seen one in place but never in any books.0 -
-
-
-
-
-
Bad perhaps, but it looks as though it's been there awhile without any expected flue or boiler deterioration.
Is there a spill switch on the draft diverter?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The near boiler piping is pretty bad as well, I'd not be surprised to hear they were having problems with fuel consumption and heat distribution.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thank you for the observations and comments. This boiler is 30-35 years old and grossly oversized at 500k input.
It is 2-pipe but not counterflow. The main vents have been removed and plugged. There are presently no vents on the system.
If I get this one, I will dig a little deeper for more information and answers.0 -
The vent connectors are SEVERELY undersized for 500 MBH input. This is not addressed in NFPA 211, '54, '31' or IFGC because up to now no one has been this stupid and desperate.
Reline the biggest flue then work backwards and calculate the maximum input for that liner and that's the maximum size boiler they can install unless they go modcon out the sidewall.2 -
How much EDR on this system?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Not on a steam system.Bob Harper said:............unless they go modcon out the sidewall.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
My guess is neither chimney has the capacity to carry the flue gases (as others stated) by itself. I'm wondering if the house used to have an oil fired boiler that was set up for forced draft, not recommended for a building with a typical thirty foot tall masonry chimney. In some instances we prefer the simplicity of the atmospheric boilers but cannot use them due to chimney constraints (this may be one of them).0
-
Oops! Wasn't paying attention.Steamhead said:
Not on a steam system.Bob Harper said:............unless they go modcon out the sidewall.
Well, in that case if you REALLY need all that heating horsepower and have two skinny flues, you would be limited to two smaller boilers that would mate with the largest liners that would fit those rough flues.0 -
Whats the draft readings? Everyone is quick to jump on it but i want to know first if it drafts? Does it spill any on a smoke test etc.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Gerry,
No tests were done. This was strictly a visual survey and estimate. It is 30+ years old so it drafts.
It’s moot point because it will not pass WSSC inspection like this. A liner is required.0 -
So whats the plan Dan? two liners, two boilers properly sized Like Bob says?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
The plan: have the chimney inspected by a licensed chimney contractor.
Ideally one boiler and one liner, if the flue chase is big enough. The house does not need a 500k input boiler. I will measure EDR and size accordingly.0 -
Are you thinking also about bouncing the EDR number in each room off the heat loss as it exists today?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements