Wiring 120v zone valves.
drooplug
Member Posts: 26
I'm installing a new system with a controller that uses 120v zone valves. I was curious about how you guys wire these up. With 24v, you can just wire nuts connections and not worry. But with 120v, you need to have them enclosed. The wire leads on the 120v zone valves aren't very long, so what do you do with the connections? Run the leads to a nearby junction box for connections to wires that go all the way back to the controller?
Who makes 120Volt zone valves?
Seems like the electrical requirements would outweigh the extra cost of 24volt!0 -
Honeywell, Caleffi, Erie, probably others.0
Line voltage are common in OEM applications, air handlers heat pumps, etc. Also commercial piping applications.pecmsg said:Who makes 120Volt zone valves?
Caleffi has 120, 208, 230 & 277VAC available.
Living the hydronic dream1 -
Usually the conduit, electrical flex or sealtite terminates at the ZV. They mostly have 1/2" KOs.
Caleffi Z-one valves carry UL 873 and also plenum & duct UL 1995 sec. 18 ratings.Bob "hot rod" Rohr
Living the hydronic dream0 -
Caleffi has 120, 208, 230 & 277VAC available.0 -
Just run "Greenfield" (flexible metallic conduit) to the valve. As HR said it will have a 1/2" knock out plug for this purpose. I've installed many line voltage zone valves. Especially nice for unit heaters, eliminates the need for an aquastat and 24v xfmr. Just use a line volt t-stat to run both the fan and ZV.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Ok. Thanks guys. When I was looking at the Honeywell, it just didn't seem like it accepted a cable clamp. You guys helped clear things up for me.0
If the valves are 120volt there is a way to wire them legally. Worse case scenario put a chase nipple inside the valve housing and mount a threaded LB or C fitting on the chase nipple. The leads will be long enough to splice in the added fitting. But I am sure you wouldn't have to go to that extreme0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 75 Pipe Deterioration
- 15.6K Strictly Steam
- 49 Job Opportunities