Rads heat when using shower
JohnCT
JohnCT Member Posts: 35
I have an oil fired boiler that heats my water and a single pipe steam radiator system. The thermostat is off but the radiators have started heating whenever I use a lot of hot water, like taking a shower. Any ideas?
    Jamie Hall Member Posts: 26,339
    Check the aquastat. It is intended that it should turn the boiler off when the water temperature reaches 160 to 180, keeping the boiler from making steam, but still allowing it to be hot enough to make hot water. It's probably failed closed...
    HVACNUTethicalpaul
  • JohnCT
    Thanks, Jamie. I’m kind of new to this. Is that a pretty easy job or should I call a guy?
    EBEBRATT-Ed Member Posts: 18,499
    @JohnCT
    I would call someone. It's either a bad aquastat, or aquastat setting is too high (you can check this, I wouldn't set it higher than 180), or there could be mud or sludge around the aquastat well (sensing element).
  • JohnCT
    Thanks, EBERATT. I have a service contract with my oil company. I’ll let them come out and bang on it with a 4 pound hammer like they do for most things.
    Steamhead Member Posts: 17,951
    You can get better service than that. Where are you located?
    Consulting
  • JohnCT
    Southeast Connecticut. Know anyone?
    HVACNUT Member Posts: 6,983
    At the top of the page you'll see "click here to find a contractor in your area".
    No, actually... but don't be afraid to look out of state -- eastern Mass. or Rhode Island. Some of the guys will work in Connecticut.