Inaccessible steam traps
bigpete638
Member Posts: 74
Many traps on campus here have steam traps that haven’t been replaced in twenty years. They are blowing through condensate pumps. Their solution was to put a trap just before the condensate pumps. What issues can this cause? Any and all information is greatly appreciated.
0
Comments
-
It will fill the returns with steam and close ALL of the traps in the building. In turn, if a radiator that has been satisfied (using TRVs) opens, no steam will move into the airbound radiator. Other radiators that are satisfied will heat through steam entering through a cooling trap and fill the radiator with water. If the room is cold enough, the radiator can freeze and split (explosively). After that, the room warms back up from leaking steam and the frozen and split sprinkler line can thaw and fill the bottom third of the building with water. Of course, if the traps worked, the tenant wouldn't have shut off the radiators and opened the window before he left for a week.
Ask me how I know....
Noel0 -
Nice description, @Noel ! And even if all that mayhem doesn't come to pass, the steam traps which haven't failed already probably will, as they are hit from all sides by confusing signals...
Not to mention that you will be spending a good deal of money on fuel which isn't doing anything to heat the structure...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
That really happened in an almost-empty 4 story dorm during winter vacation. None of that is exaggerated.
Noel0 -
Oh I believe you -- all too well.Noel said:That really happened in an almost-empty 4 story dorm during winter vacation. None of that is exaggerated.
NoelBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
nothing is inaccessible, it's just a matter of how much havoc it causes to get to the traps. Maybe you can remove the guts to the existing traps and install a new traps down stream in an accesable location.0
-
@bigpete638, What you describe is called MASTER TRAPPING, which is a definite no-no. The details are fully explained in THE LOST ART OF STEAM HEATING, pages 31, 163, 174, 182, and 187.
These pages just say in different words, and with different detail, what @Noel said.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.-1 -
You guys are amazing! There is asbestos involved which also limits access to many traps as well.0
-
Thanks again!0
-
Yep, and once you get to them the customer now knows better than enclose them.EBEBRATT-Ed said:nothing is inaccessible, it's just a matter of how much havoc it causes to get to the traps. Maybe you can remove the guts to the existing traps and install a new traps down stream in an accesable location.
I have cut open many walls & cabinets in my career to access stuff. Not just traps.0 -
The asbestos needs to go and re-insulate.bigpete638 said:You guys are amazing! There is asbestos involved which also limits access to many traps as well.
Around here you are in deep stuff if you disturb it so abatement is job 1.0 -
And may I point out that in general traps should not be insulated? They need to be able to cool, at least a little, to release condensate (radiator type traps, that is, or anything with a thermostatic element).Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I had to remove a corner cabinet to find the pipe tunnel opening. I was sure the F&T was there as I had the original prints from 1955.
The cabinet was installed in the 1970's. I am fairly certain the trap was not serviced since the original install. It was blowing steam into the cond pump and one of the pipes had lost the threads and was leaking water.
One thing about removing the guts and installing another F&T is the drop from inlet to outlet in my case was very little. The piping had just about run out of slope for returning condensate.
There should be some drop to establish flow IIRC.
So Pete, if you have a nearly level outlet pipe you might reconsider just adding a trap downstream.
0 -
@JUGHNE
Tunstall has some inline F & T traps which can get you out of a jam, but I agree there has to be some drop to get the condensate away from the equipment0 -
Milwaukee tool compa ny has made it their mission to ensure that no steam trap is inaccessiblegwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
I forget to check back with the site. My apologies. Thank you again for everyone’s insight. It’s invaluable!0
-
> @gerry gill said:
> Milwaukee tool compa ny has made it their mission to ensure that no steam trap is inaccessible
Hi Gerry. Can you elaborate? Thanks.0 -
Sawzall Time!STEAM DOCTOR said:> @gerry gill said:
> Milwaukee tool compa ny has made it their mission to ensure that no steam trap is inaccessible
Hi Gerry. Can you elaborate? Thanks.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
That they have, the sawzall is a great tool.gerry gill said:Milwaukee tool compa ny has made it their mission to ensure that no steam trap is inaccessible
0 -
Hi BigPete638! Scott Malo here from Tunstall corporation. I agree with most of the folks here in that even if a steam trap seems inaccessible, there are creative ways to get them and people willing to take the plunge. (Initiation here at Tunstall is about 1,000 hours of tunnel crawling ). Master trapping is definitely not an alternative. I am unsure how many you have that are buried but if it has been that long, there is a good chance they are leaking or just blowing by. We can definitely provide you with the right material for repairing or replacing them and might even have some recommendations or referrals for some companies that would be willing to do the survey and actually perform the repairs. We also have a 10-plate bellows that could be part of the face-plate repair kits which would extend the life of those traps and put some additional in between needing to revisit them. I am happy to communicate with you via email if you want to continue the discussion. I can be reached at smalo@tunstall-inc.com. Cheers!1
-
Thanks again everyone. Another issue is the amount of asbestos and the unwillingness to spend the money for removal. This the traps not being changed. Even the price of trap replacement has been a deterrent. It’s that crazy here. Sorry for the late responses. I was hoping to get email notification of any new messages on here. Things get hectic and I forget to check. Again I really appreciate all the information. This site is amazing.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements