New radiant loop interferes with old one
dori
Member Posts: 16
Original system is a 1950 radiant 1" pipes in ceiling. In the sketch below, this is the loop with the two parallel recirculators. The feed from the mixing valve is 1 1/2". The return is 2" . The zones from the main are fed with declining pipe diameters, with the last one 3/4". The returns of the main loop connect to the 2" return all along the way, with the furthest about 60' away from the boiler room.
The system was converted from an open air expansion tank to an air-out closed system as shown. The pressure is set at 15 psi. The single loop on the right is for cast iron radiators on second floor. There seem to be no issues with that loop.
The newer loops are a 3/8" pex radiant floor and a kick space heater, both in the kitchen and both very close to the boiler room.
When the radiant loop in the kitchen is active, the main loop is mostly cold -- especially the far branches.
Under suspicion is how the expansion tank is connected to the system although the interaction dates before the tank was added.
Thanks for any advice.
The system was converted from an open air expansion tank to an air-out closed system as shown. The pressure is set at 15 psi. The single loop on the right is for cast iron radiators on second floor. There seem to be no issues with that loop.
The newer loops are a 3/8" pex radiant floor and a kick space heater, both in the kitchen and both very close to the boiler room.
When the radiant loop in the kitchen is active, the main loop is mostly cold -- especially the far branches.
Under suspicion is how the expansion tank is connected to the system although the interaction dates before the tank was added.
Thanks for any advice.
0
Comments
-
What, if anything, is powering flow through the kickspace and radiant floor? Am I missing something?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
-
The sketch shows pumps on the returns from those zones. It's piped the old way.Jamie Hall said:What, if anything, is powering flow through the kickspace and radiant floor? Am I missing something?
I'm guessing the pumps are fighting each other somehow but it's difficult to know without model numbers at least.
If the expansion tank is in question just get the system up to temperature and shut the valve on it. Run everything and see what happens. Shutting the valve makes like it's not there.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
I must be blind (you don't have to agree..) but I still can't see what pump or pumps is driving circulation in the kitchen floor/kickspace loop...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@Jamie Hall
all the way to the left the blue riser coming from the kikspace heater has a pump in it (I think)0 -
It's piped incorrect , when the kitchen calls for heat it opens a boiler bypass ..Mr Hall is correct , no Circulator or pressure drop for kitchen , assume only a zone valve is used on the kitchen . You would need to add a circulator and a check . The other zones would need a check as well .. .. Reverse return and pumping away are other issues
There was an error rendering this rich post.
0 -
Also if your return sensor is affecting any of the heating, it's not picking up the return temps from the 2 kitchen zones.
You also seem to have a lot of air elimination, and a lot of y strainers.
Wouldn't be the first time, right?Zman said:They are smaller pump symbols on the return side.
It looks like the OP @dori is "one and done" we are just talking to ourselves and I am good with that.There was an error rendering this rich post.
0 -
Maybe I am the one who's blind. Sure looks like a pump to me on the kitchen loop.
But we are all commenting and the OP hasn't returned0 -
Oh yeah. Sorry. Now I see them -- two tiny pump symbols, one for the radiant and one for the kickspace heater. Getting old has its problems, folks. Ain't for sissies.
And I don't even want to get into figuring out the relative flows and headlosses in the circuits...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@Jamie Hall Having issues myself. As far as flow and head loss I wouldn't have a clue. You read my mind0
-
Sorry guys for having initiated the discussion and then disappeared. I was never notified of your postings by the Wall, and I assumed as a newbie that no one came to my rescue.
I did move the expansion tank to the other side of the recirculators of the Main loop. It helped like magic for a week, but 2 weeks later the system is air locked. All my attempts to flush the air have failed to take hold. The heat is resumed for a day and next morning it is no-show or partia-show.
The problem with the Kitchen loop (pex) was solved by adding a Spirovent on the supply side. Never had an issue thereafter.
I just posted a new thread. If you wish to respond, please use that one.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements