How do I know the system circulator is the right fit
Le John
Member Posts: 234
I have roughly 75 feet of baseboard over three separate zone valves. How do I select the best circulator?
Zone 1 26 feet
Zone 2 18 feet
Zone 3 30 feet
Zone 1 26 feet
Zone 2 18 feet
Zone 3 30 feet
0
Comments
-
-
btu's of the zone divided by 500 x delta tee ( that gives your g.p.m. )
then to get your head pressure you take the total length of pipe (longest zone) then you multiply by 1.5 elbows and other fitting) divided by .o4 that will give your feet of head.
then use the charts of the pump manufacture to give your pump size .
file:///C:/Users/u192772/AppData/Local/Temp/SelectingCirculators-1.pdf3 -
That's really odd. How is this piped? Is it a monoflo system? Maybe all of the baseboards are run in a home run to a manifold at the boiler?0
-
@SuperTech 3 separate zones - each with a supply and return. The piping in the walls are 1/2 inch.0
-
-
-
@SuperTech - a Grudfoss UPS1558FRC circulator as the system pump feeding three Honeywell Zone Valves. I'm not at the property today but will post pictures when i get back there on the weekend.1
-
Probably estimate the distance but guesstimate the fittings. I think Taco suggests a multiplier piping length X 1.5 to get a ballpark #Le John said:@hot_rod how do I calculate the length of piping, number of fittings that are in the walls?
The majority of the time a small multi speed 15-58, or other brand equivalent, covers a wide range of residential applications.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Why 1/2" Supply and return lines?0
-
There is nothing wrong with using 1/2 pipe to smaller zones. We do it all the time with panel radiators. As long as you have adaquite flow per the zone size (30' fin tube in your case). The smaller piping does create extra head, but most residential size systems are short enough that most reasonable sized circulators have no problem supplying the required flow.
No reason to always use 3/4 pipe, it is just most commonly used.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!1 -
Thanks @Solid_Fuel_Man so is the Grundfoss UPS 15-58FRC a good pump for the application? I thought based on the formula above I needed something like an Alpha 2 1558 or a Taco VT2218?0
-
Both pumps are you mentioned are great and can cover a wide range of flow requirements. I'm a fan of both pumps but I have found that the Alpha is great for zone valve applications.I suppose that just because the 1/2" pipe is unusual doesn't make it completely wrong.0
-
There is nothing wrong with 1/2" supply and returns, especially since your largest zone is only ~15k/btu.
If your 15-58 is working well, I don't know that I would bother changing it. You can set it on the lowest speed that will give you satisfactory heating. A 20 degree supply/return delta t would be a good indication.
The other circs you mentioned would be a nice upgrade and would save a few bucks in electricity."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I bet even on the lowest setting, there the delta T will be less than 10 degrees.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
with about 70 feet of baseboard with a 15-58 on speed 1 - getting between 7 and 8 as a delta T when all three zones call for heat. I'm wondering if switching to a lesser pump like a TACO 003 or 006 would increase the delta T? The Lochinvar Noble needs 5GPM minimum flow (I think).
System heats just fine just trying to get a higher delta T.0 -
That 20 degree delta is based on your design day conditions. Were you at or near those conditions when you took the measurements? On any warmer day your delta will be smallerYou can have it good, fast or cheap. Pick two0
-
@Le John
Just check the temperature in and out of the baseboard on each loop.
If your TD is less than 20 and it is heating the house as you have indicated then your fine. Check this with all zones calling.
If you can balance the flow between the zones (based on inlet and outlet temperature) I would do that but I would not choke the flow to get to 20 deg TD. Boilers last longer with enough flow
I wouldn't go looking for trouble0 -
Is the system heating OK? Keeping up on design days? Do you have boiler short cycling issues? Turn all the stats down, let the ambient drop to 68 or lower, fire up and measure delta. 20 or higher?
Observe for 30 minutes, I suspect it will continue to drop unless you are at design temperatures outside.
Don't get too hung up on delta T across the system, it can and will move around. If the system is near shutting down, satisifing the load, expect that delta to close up
It will go to 0 when then load is satisfied
If it is direct piped you will only be able to run the gpm down to the point that Lochinvar allows, more you may end up going to high limit on the boiler. Really no reason to operate the boiler by bouncing off high limit.
Here is a good read explaining how heat transfer works and the truth about delta T.
https://www.caleffi.com/sites/default/files/file/idronics_23_na.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements