Heating bathrooms with one pipe steam system
Burnham IN7 in the basement heating 3300 sq ft.
I could run steam pipe into both bathrooms, but I wanted to know my other options. Small steam baseboard, etc.
Thanks
Comments
-
Small cast-iron radiator, as made by OCS, Governale, Burnham etc.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Anything with a more modern appearance?0
-
-
Other option is run a hot water loop off the boiler. Has ot be piped correctly. But if you have floor access under it, you could do a low temp radiant floor. But you need a mixing valve and injection loop to control water temp.
Can also custom build a radiant panel if they have a shared wall. Add some towel racks and you also get a towel warmer out of it.
When I renovate our bath, I wish I had piped the shower hot water supply in series with a towel rack made from copper pipe, but before the recirc connection. I’ll do it on our master bath when we construct it.1 -
Sounds like a radiator is the most straightforward way.
Found a nice small one at AF Supply.com And they have a location very close by!
https://www.afsupply.com/cast-iron-radiator-19-h-4-tubes-4-sections.html
Thanks.
0 -
I could sell you mine, I just swapped it out for a vintage model
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
steamradiators.comgwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
What's the EDR on the radiator and the measurement? Thread size on the radiator valve? Thxethicalpaul said:I could sell you mine, I just swapped it out for a vintage model
0 -
-
Does a bottom tapping of 1 1/4" hook up to a 1" steam radiator shutoff valves?
I ask b/c I have radiators the same size 19/4.5/17.5 and they take 1" steam radiator valves.
I'd like to order the required piping today.
Here's the radiator I'm considering.
https://www.afsupply.com/cast-iron-radiator-19-h-4-tubes-4-sections.html0 -
Just get a 1-1/4"x1" bushing and you'll be fine.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
That is the exact same radiator @branimal and the bottom connection is 1-1/4”. A bushing would work as @Steamhead suggested, although I like bushing the bottom of the radiator valve instead.2
-
I'm reducing a 2" steam pipe and splitting it off to these 2 bathroom radiators. Would it be preferable to run 1" or 1 1/4" piping after the reducer coupling? See diagram.
Thanks!
0 -
I'd go 2" all the way up to the tee, and make your reductions there. Much simpler and no chance of inadequate steam delivery as long as all your horizontal pipes have good pitch.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
I got mine from AFSupply too, just up the road from me in Fairfield NJ if I recall correctly. I can tell you that even though it is pretty heavy, it gives off nothing like the heat that the old ones do.
I can't even imagine how little a 4 section one would give off, I think it wouldn't even be noticeable!NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
I was talking to a landlord in my area and he said none of his bathrooms have heat. It's not required in NYC either. And he suggested cast iron radiators in a bathroom are going to rust from the constant moisture (shower etc).
Another option is to put a radiator on the wall just outside the bathrooms. It will heat up the kitchen area while also giving off some heat to the bathrooms. See pic.
@Steamhead - Regarding pitch, If I put a 90 elbow on a vertical pipe, you cannot create any pitch unless you lean the pipe backwards? Is it better practice to put a 45 elbow on vertical pipes?
@ethicalpaul why do you think these new radiators don't give off as much heat? Is the metal different? Or the new radiator's internal pathway for steam smaller?
0 -
I'm not sure why, or even the extent of the difference (it's hard to measure objectively). The tubes are definitely smaller than older radiators, and yet the units definitely have a lot of mass, and that could mean the internal races are very small. The unit got hot to touch, but it didn't seem to "radiate" heat very well. I never got around to painting it, and that can make some difference.
The rust concern I think isn't really valid. I have a (painted) in-wall cast iron radiator/convector in my house (built 1913) and there's no rust (and there's never been a bathroom fan in there either). Certainly with modern venting codes there must not be "constant moisture" in these bathrooms.
I can tell you the comfort of a heat source in the bathroom is very nice in the winter.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I have a small radiator, about 25 EDR in each of two bathrooms in my house and they keep those bathrooms nice and toasty. They are original to the house (117 years old) and moisture has had no effect on them so the concern about showers/other bathroom moisture is unfounded.
I also have two other bathrooms that don't have radiators at all but have radiators in the hall nearby. Those bathrooms stay very comfortable also but not as toasty as the ones with radiators.3 -
-
I live in Manhattan and I've only got a steam riser in my bathroom. A 2" riser pipe at 1 psi steam pressure gives us a surface temperature of about 215° at roughly 1 EDR per linear foot. With a 9' ceiling, that's basically a Governale/OCS/Burnham 4-tube, 19" tall radiator with 6 sections.
Rust in not an issue. Spray paint the radiator if you're concerned. And having the radiator outside the bathroom will be no help at all. Don't listen to the ridiculous things people want to tell you.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes3 -
@JohnNY , It's not worth a debate but I have two bathrooms that stay quite comfortable without radiators in them and the radiators outside those rooms are the only source of heat. It's not ridiculous. It does however assume you leave the bathroom door open when not in use.0
-
Fair enough.Fred said:@JohnNY , It's not worth a debate but I have two bathrooms that stay quite comfortable without radiators in them and the radiators outside those rooms are the only source of heat. It's not ridiculous. It does however assume you leave the bathroom door open when not in use.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Thanks for the feedback guys. Right now I'm renovating the 3rd floor of a 3-family building. I'll be completely demo'ing and renovating the 2nd floor after I'm done with the 3rd.
My thinking is, if I need bathroom radiation, I can always run the pipes up from underneath when I have the 2nd floor ceiling open. Laying pipe from up top is a bit tedious. Laying on joists and reaching down 2-3' with pipe wrenches is tough on the body.
The added benefit is I'll know exactly where the finished walls are.0 -
Had a old cottage home that just had a 1 1/2 pipe coming out of the floor went about 7 ft up w a cap and a angle vent drill and tapped into the side of the pipe . Barely noticed it kinda behind the door heated that bath pretty good .it would have been nice with a couple of tee s off it to hang towels . The house was built in the late 40 s or so all original .peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
I like what @gerry gill did on one of his mini tube installs. That custom box0
-
Nothing nicer than a warm radiator in the bathroom. I have had many through the years, hot water and steam. I've never had a problem with a radiator rusting in a bathroom. BUT, if you get in the habit of putting wet towels, mittens, etc on the radiator to dry, you're going to get rust from that. Hang towels on a rack directly above the radiator.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements