Steam boiler gauge correct? Seeking advice to optimize performance and eradicate water hammer
Comments
-
I have a concern that your pressuretrol isn’t wired correctly into your other control wiring.
You might:
- Power down the boiler
- Disconnect either one of the ptrol wires, leave it hanging in the air
- power up the boiler
- turn up the thermostat to make it ask for heat
The boiler shouldn’t fire up. If it does, then the boiler is ignoring the ptrolNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Also, does that gauge rise from zero during the heat cycle to that point? Does it go higher?
The piping looks OK but with it being a Dunkirk, we all wish they had piped both steam supply ports.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
I doubt you are operating at 12 psi. If you were, you'd hear your radiator vents screaming well before then.
You can easily check the accuracy of your pressure gauge. Is that a nipple and valve (with the yellow handle) attached to your sight glass? If so, put a hose barb into the bottom of the valve and attach some clear vinyl tubing. Run the tubing up to the floor joists above, and leave the top end open. Then fire up the boiler and open the valve the tubing is attached to.
The difference between the height of the water in the tubing and in the sight glass indicates the pressure in the boiler (28" = 1 psi). See how high the water goes in the tubing before the boiler shuts off on pressure. Shouldn't be more than 60" if you have your Pressuretrol turned down all the way (and it is working).
But be careful. If the water in the tubing starts rising too much you'll have to turn the boiler off or get hot shower of boiler water.
1 -
-
0-30 gauge is not that accurate, but usually not off by that much, if they still work. That is that it will start at 0 on cold start and takes a while to build up any pressure and then slowly goes up.
Get another guage on the pigtail. It is a very easy job, took me less than 10 minutes to put everything in and it was my first time doing it for my boiler.
1 -
Thank you. I'll have to do the wire test mentioned above, and see what happens. When the boiler fires up from cold, the gauge starts at zero. The funny thing is, it takes a long time for the needle to drop back down to zero, when the heat is off. There could be no more steam pressure left in the system, but it will read 5 pounds, and gradually decrease.0
-
I think that would point to a clogged pigtail or gunked up ptrol, but I know you said you fixed both of those possibilities, so it's a puzzler to me.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
When the boiler fires up from cold, the gauge starts at zero. The funny thing is, it takes a long time for the needle to drop back down to zero, when the heat is off.
This tells you the gauge is not working properly. When the boiler is shut off, the gauge should return to zero (or less if it can read vacuum) within a matter of seconds.0 -
How much water do you have in that boiler? It looks pretty full. Those side tap boilers should not be more than half, maybe 2/3's full (if both sides are used. With just one side in use, water in the boiler will tend to push to that side so I'd keep it at about half full..0
-
Define "long time". As sort of a rule of thumb, a moderately large system can be expected to drop around a pound to a pound and a half a minute -- but not seconds. But it's quite variable.Chris_L said:When the boiler fires up from cold, the gauge starts at zero. The funny thing is, it takes a long time for the needle to drop back down to zero, when the heat is off.
This tells you the gauge is not working properly. When the boiler is shut off, the gauge should return to zero (or less if it can read vacuum) within a matter of seconds.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
So I tried the wire test suggested earlier by Paul, and disconnected one wire from the pressuretrol, and tried to run heat, but the boiler wouldn't kick on, so that eliminates a bad pressuretrol or it not being wired correctly.
I haven't monitored the gauge for longer than a few minutes, but it definitely doesn't drop to zero that quick....maybe takes half an hour or even more. Seems like my gauge isn't working properly.
Do you think there is too much water in the boiler? Currently the water level is a little below half on the sight glass. I do get two or three radiator vents spitting water on the radiators in the rooms furthest from the boiler.0 -
@ChrisF, have you seen this video?
https://heatinghelp.com/systems-help-center/wet-steam/
Isn't that the same boiler (possibly rebadged) as yours, with the steam coming out of the side not far above the water line?
Try what @Fred says, maybe even a lower water level, and see what happens with your banging.
@Jamie Hall I don't think we disagree. When I said the pressure should go down in seconds, I wasn't thinking single digits. If the boiler is running at less than 2 psi, I'd say 90 seconds is seconds not minutes. (Mine goes down to zero much faster, but I never exceed 1/4 psi).
0 -
@Chris_L , Wow! That is a lot of wet steam being produced!! I'm wondering if I have the same problem? However, if I drain some water out of the boiler, it won't want to fire up, and the (low water) red light comes on, on the low water cut off. The boiler will come on, only
after I add more water.
@ethicalpaul I saw your wet steam video. Hoping I don't have that same kind of issue.1 -
@Chris_L -- yes, 90 seconds sounds reasonable. Cedric drops from 7 ounces to 2 ounces in the length of time the burner goes through its post purge... which is about 30 seconds.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@ethicalpaul I saw your wet steam video. Hoping I don't have that same kind of issue.
It's not actually too horrible of a situation, and probably fixable for not much cost or effort if you do. Your piping is way better than mine and I have mine a lot better now. Even when mine was throwing all that water into the main, I had no spitting vents, nor any other noticeable problem, due to good main venting which you should also check into if you haven't. Contrary to popular belief, steam heat is VERY forgiving and it usually takes several bad things stacked up to result in poor performance.So I tried the wire test suggested earlier by Paul, and disconnected one wire from the pressuretrol, and tried to run heat, but the boiler wouldn't kick on, so that eliminates a bad pressuretrol or it not being wired correctly.
It does look good for the wiring, that's great! But the only full test for the ptrol is to get your pressure high enough to trigger it. It may still not be activating on pressure, but it being a new one I think the odds of that are slim. A new gauge should help you get to the truth. You're going to get a 0-3psi one I hope, to test with at least temporarily, then code dictates you have to have a 0-30 one on there. You can mount both if you feel like it.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements