Hydronic system pressure increase issue need help with.
JHilpipre
Member Posts: 6
Looking for some help identifying a problem I ran into yesterday that has my well... STUMPED!
Scenario:
- Assisted Living center with (5) 1992-1994 C.I. boilers and 1 Weil Mclain condensing boiler.
- 3 boilers have failed (leaking) in past 4 weeks.
- There had been an aluminum mod/con installed 2 weeks ago and was informed it had already failed a week later and a warranty replacement had been installed.
- System pressure increases from 15-25 psi throughout the day and maintenance person has been removing water from ceiling mounted compression tank multiple times daily so relief valves do not open up.
- The tank has a B @ G Airtol fitting connected to bottom of tank of which is connected to top of Roll Air eliminator.
- The make up water is totally isolated with (2) inline ball valves as well as RPZ inlet/outlet valves turned off.
- The inlet pressures to all (4) loop circulating pumps are in a positive pressure.
- System is being controlled by a Tekmar and SWT does not exceed 180 I am told.
- What in the world could cause something like this?
Thanks for any and all input!
Jim Hilpipre
Scenario:
- Assisted Living center with (5) 1992-1994 C.I. boilers and 1 Weil Mclain condensing boiler.
- 3 boilers have failed (leaking) in past 4 weeks.
- There had been an aluminum mod/con installed 2 weeks ago and was informed it had already failed a week later and a warranty replacement had been installed.
- System pressure increases from 15-25 psi throughout the day and maintenance person has been removing water from ceiling mounted compression tank multiple times daily so relief valves do not open up.
- The tank has a B @ G Airtol fitting connected to bottom of tank of which is connected to top of Roll Air eliminator.
- The make up water is totally isolated with (2) inline ball valves as well as RPZ inlet/outlet valves turned off.
- The inlet pressures to all (4) loop circulating pumps are in a positive pressure.
- System is being controlled by a Tekmar and SWT does not exceed 180 I am told.
- What in the world could cause something like this?
Thanks for any and all input!
Jim Hilpipre
0
Comments
-
Are they making domestic hot water with indirects, or coils on the boilers?0
-
How is the air cushion in that expansion tank being maintained? Is it a diaphragm or bladder type tank, or is it a hyrdopneumatic? If it's the latter, are the air controls actually working? Is there any other air eliminator on the system?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
-
There are no indirect water coils or heat exchangers in this system.
It only provides heat distribution through baseboard radiation, fan coils and reheats in VAV's.
0 -
I'll go back to the compression tank. Check the air cushion in it. The airtrol may have failed...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Water logged tank is all that’s left I suppose.0
-
The only logical explanation for this would be issues with the compression tank. Maybe the failure of so many boilers is an indication that it's time to update the boiler piping to modern expansion tanks and air eliminators, preferably the microbubble resorber type. This should have been considered when replacing the first boiler.0
-
The compression tank has a sight glass and appears to be at 2/3rd level.
I TOTALLY agree it is time to redo the system and am putting a proposal together but need
to remedy pressure issues til end of heating season.
The tough part is answering the question "why did it work fine until this year"? When I do not know that answer.
On another note, I am having the water tested to see if any issues there causing failures.0 -
Okay one last thing. It’s filled to the correct level, but is it the right size? How many boilers were added from the original configuration with out changing the x tank size?0
-
Are the valves open to the sight glass? They are sometimes shut off if leaking.
You mention reheat, is there any glycol involved?0 -
The level could appear correct but if a valve is shut off or the airtrol fitting is plugged up the compression tank won't do it's job of regulating system pressure.0
-
Yes, valves are open but there could be blockage in them causing gauge glass levels to be inaccurate. I did not drain tank, remove and inspect them that day.JUGHNE said:Are the valves open to the sight glass? They are sometimes shut off if leaking.
You mention reheat, is there any glycol involved?
There is glycol involved.0 -
Are the make up water valves closed? What kind of valves are they and is one of them failed? That's where I'd start.Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0
-
Even if the valve has failed, and is allowing water when system is at the prvs setting then it’s the prv.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements