How do I take off the Pigtail to clean it
ksd99
Member Posts: 77
Hi,
I purchased an old house and I want to make sure the pigtail is not clogged, I look at the broiler and cannot figure it out, I bet you guess I am mechanically challenged. I would let a professional do it, but there are none in my area of Michigan. I better learn and take control. Any help would be appreciated.
I purchased an old house and I want to make sure the pigtail is not clogged, I look at the broiler and cannot figure it out, I bet you guess I am mechanically challenged. I would let a professional do it, but there are none in my area of Michigan. I better learn and take control. Any help would be appreciated.
New owner of 1 Pipe Steam Boiler - learning all I can- no real steam pro in S.W. Michigan - if you know of 1 -let me know.
0
Comments
-
Post a picture from a ways back?0
-
Here you go, I plan on doing it tomorrow. I am not mechanically incline so it will be a challenge.New owner of 1 Pipe Steam Boiler - learning all I can- no real steam pro in S.W. Michigan - if you know of 1 -let me know.0
-
Picture doesn't seem to be attached
Also, if you're not mechanically inclined, you might want to wait until it's not bitterly freezing cold where you are...my pigtail broke when I removed it for the first time after I bought the house.
Also welcome from a former West MichiganderNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Here you with the pic.....it’s actuslly going to be 30 tomorrow. Heat wave. I so want to clean it and if I do break it I have a new one just Incase. I also wanted to installment gauge. Let’s see if I can post the pic.
Ii amactuall from Chicago but I have a home in mich.New owner of 1 Pipe Steam Boiler - learning all I can- no real steam pro in S.W. Michigan - if you know of 1 -let me know.0 -
I am going to clean the water glass too. The water is clear but there crud on the walls of it.New owner of 1 Pipe Steam Boiler - learning all I can- no real steam pro in S.W. Michigan - if you know of 1 -let me know.0
-
Oh now that's just not kind. Is there enough room to turn the pressuretrol where it is? And enough to turn the pigtail when the pressuretrol is off? What you need to do is take the cover off the pressuretrol and make note of where the wires go. Then with the power off to the boiler take the wires off and take the pressuretrol off the pigtail, then pour water into the pigtail -- if it flows through easily, stop right there and reassemble the whole thing. Otherwise, you can try running a wire through the pigtail -- or just take it off and put the new one on. If there is enough room to swing it. From the picture I can't tell -- but it may be close.
On the sight glass. I'd leave it be until summer. Then make sure that you have a new glass on hand and the little O-rings which seal it at the top and bottom. They are unbelievably fragile and, as I just said on another thread, I make it a policy to never reuse an o-ring.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
Thank you.New owner of 1 Pipe Steam Boiler - learning all I can- no real steam pro in S.W. Michigan - if you know of 1 -let me know.0
-
Unless you know the pressuretrol isn't working right, I wouldn't suggest trying to take the pigtail off, particularly in this weather.
It looks like it is brass. It is above the water line. It is very unlikely to be clogged.
You can easily check. Take the cover off the pressuretrol. Turn the wheel down as low as it will go (1 or lower). (Looks like you've got the cut-in as low as is an go, which is good.) Turn the heat up--3 or 4 degrees. The system should build pressure. Watch the pressure gauge. See what the pressure is when the boiler shuts off.
If you are right next to it, you'll hear a click when the pressuretrol shuts it off. If the gauge reads 2 psi or less when it trips, the pigtail is unlikely to be clogged. Nothing more to do.
As for the sight glass, you don't need to take it apart to clean it. Close the two valves at the top and bottom of the glass, and take off the plug on the bottom. You can then (carefully) clean it from below. If you get a small ball valve to replace the plug, you can periodically open it while the boiler is running to clean the glass.
0 -
Could be the angle of the picture but that could be challenging.
When you want to remove the pigtail IF YOU FIND THE PRESSURE CONTROL WONT SPIN OFF DUE TO HITTING THE JACKET then do this:
take the wires off as @Jamie Hall mentioned
take a small pipe wrench or Channelocks and loosen the pigtail just a bit to break it loose
Take a hacksaw and cut through the pigtail....leave an 1 1/2" pc coming out of the tee. Now you have the ptrol and cut pigtail in your hand. Removes the small pc from the tee.
Install a 1/4" brass union on your new pigtail and a 1/4 x 1" brass nipple into the tee. Then you can reinstall the whole thing without turning it
0 -
Maybe the maintenance guy didn’t do it because of it. This concerns me.New owner of 1 Pipe Steam Boiler - learning all I can- no real steam pro in S.W. Michigan - if you know of 1 -let me know.0
-
It's not difficult. Wait for a day with moderate temperatures. Have the tools and parts and do it0
-
From the scratches on the jacket it looks like the pigtail will unscrew. Also there is blue Teflon tape on the joints.
So it looks like it did come off and go back on.
If the P-control will hit the jacket, you can tighten the pigtail slightly and that will roll the control towards you giving more clearance. Reverse the procedure to reinstall.0 -
Thanks all.New owner of 1 Pipe Steam Boiler - learning all I can- no real steam pro in S.W. Michigan - if you know of 1 -let me know.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements