Boiler relay board making noises
klin816
Member Posts: 2
in Gas Heating
Hello,
I have a gas 2 zone boiler and when A zone's thermostat turned on, everything runs smoothly but when B zone's thermostat turned on, sometimes, caused the small relay boxes on the relay board to make a fast clicking sound, which turns the boiler on and off. What's the problem? Do I have a bad relay board? Wrong wiring between the thermostat and the relay board? How can I solve this issue? Are there other causes to the issue? Thanks!
Kevin
I have a gas 2 zone boiler and when A zone's thermostat turned on, everything runs smoothly but when B zone's thermostat turned on, sometimes, caused the small relay boxes on the relay board to make a fast clicking sound, which turns the boiler on and off. What's the problem? Do I have a bad relay board? Wrong wiring between the thermostat and the relay board? How can I solve this issue? Are there other causes to the issue? Thanks!
Kevin
0
Comments
-
-
Also check all the connections and wiring -- and thermostat. If you are losing signal voltage anywhere along the line that can cause the problem.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
what's the brass looking dohickey at the bottom?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Current relay??
Rick0 -
@Docfletcher I can try swapping the relays but I did change a new relay for Zone B but it didn't do anything.
@Jamie Hall Do I call an electrician or a heating repair guy to check the wiring? I don't have any knowledge about a boiler.
@hot rod_7 I have no idea tbh. This is the setup when I bought the house.
@rick in Alaska What do you mean by "Current relay"?0 -
That's a good question, @klin816 . Ideally, either one should be able to check that you are getting the correct voltage at the relay -- probably but not certainly 24 VAC -- and then, if you are not, track down which wire or connection or other device is causing the problem. Ideally. In practice... perhaps a really good electrician with some imagination is the better bet, but I wouldn't want to lay odds on it either wayBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If you get chattering when both zones are calling you can try...
Turning zone A off and have zone B call for heat. Does it chatter now?
0 -
Is the thermostat for zone B heat only, or A/C also?
Nest thermostat?
On the Argo board does the zone B thermostat wire go directly to the thermostat or to an air handler or relay first?
With the slot screw terminals you can tell it's an old Argo and the problem could be internal.
Most times I get a call for a chattering cube relay, its usually a separate 24v source butting with the transformer in the zone board.0 -
Could the circulator wiring run thru the current relay?
Seems to be the only thing to draw enough current to activate it.
T-stat does a relay to start pump, current relay starts boiler??
Seems pretty strange if that is the case.0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements