Air Venting for Pipe Radiators

JohnNY
JohnNY Member Posts: 3,293
edited January 2019 in Strictly Steam
I got into a nice project in Tribeca, NYC with a 5-story building that was converted from warehouse space to very expensive residential living spaces. The original 2-pipe air vent system remained in place and it consisted of over 200 feet of 1-¼" steel pipe in each apartment terminating with an air vent. No traps.
The residents tried lots of different plumbers who suggested different types of vents and control settings but imbalance and overheating was what they lived with for many years.
After having good experiences with 2-pipe air vent systems and TRVs with oversized vents recently, I gave this a shot and it worked really well.
Instead of the usual little ⅛" (4, 5, 6, ,C, D, 41, etc) vents, I decided to go with ¾" thermostatic valve bodies and main vents on each 100-foot-long pipe radiator. It's working really great. I'm very happy with it and so are my clients.
Some of what was existing. Sorry for the giant pics.




Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes