flow in fin tube baseboard heat
mdwdrw69
Member Posts: 1
Does running more than 4gpm in a standard high output fin tube base have any effect on the maximum output
Or is the maximum achieved at 4 gpm and anything faster just stays capped at the maximum output
Or is the maximum achieved at 4 gpm and anything faster just stays capped at the maximum output
0
Comments
-
The only thing changing flow rate will do -- within reason, that is -- is change the delta T across the radiation. In principle, a smaller delta T, for a given input temperature, will give slightly higher output, since it is the average of the input and output temperatures which determine the output.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
plus velocity wear and noise at high flow ratesBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0