Boiler Overheating

mstarbird
mstarbird Member Posts: 10
This boiler is been having issues off and on for months. 6 months ago the watts pressure regulator with backflow preventer was replaced and the expansion tank and valve above it was also replaced. Now the boiler is pegging out at 240 again every time it turns on. The Honeywell is set at 210 on the high end trying to prevent it from getting to hot. Worked for a few hrs but it's again up to 240. The pressure is at 25 which is also up. I checked the screen on the watts and it's clean. Could the new pressure regulator be bad already?

Comments

  • mstarbird
    mstarbird Member Posts: 10
    Also the boiler is a Biasi b series with a Riello 40 burner. System is 14 years old.
  • Ironman
    Ironman Member Posts: 7,521
    More info needed. How about some pics? What make and model boiler.

    But no, the fill valve will not cause the temperature to go too high; your aquastat is not functioning correctly. There may be other issue too.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Gilmorrie
    Gilmorrie Member Posts: 186
    This is a hot-water boiler? In my opinion 210 deg F is too high for the aquastat. Try 170 deg.
    Ironman
  • mstarbird
    mstarbird Member Posts: 10
    Boiler info was posted above. Temp also continue to climb 30 degrees after boiler kicks off. Aquastat was turned down to 210 after the pictures of the face plate was taken.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,327
    Set you high limit aquastat at 190 deg. The water pressure will change with the water temperature...this is normal about 12-15 psi when cold 25 is ok when hot with a properly functioning feeder and expansion tank it should not go much over 25 as your relief valve may open.

    One question: The city water should feed through the backflow preventer first and then through the water feeder to get to the boiler....check that

    Also with the aquastat set at 190 it should shut the burner off at approximately that temperature. If you pumps shut down with the burner you temperature may rise above the 190 set point by 5-10 degrees due to residual heat trapped in the boiler. this is normal
  • mstarbird
    mstarbird Member Posts: 10
    One of the reasons I was leaning towards the watts pressure regulator was I drained off a bunch of the pressure and when I lift on the blade it's not feeding or seeming to not be feeding the way it should be. Pressure isn't changing and no noise is being made.
  • mstarbird
    mstarbird Member Posts: 10
    The water system is off a well. It's not city water. One of the reasons we checked the screen on the watts. But it was clean as a whistle.
  • Ironman
    Ironman Member Posts: 7,521
    All of those circulators need to be rotated so the motors are horizontal. They'll fail they way they now are because the bearings won't be properly lubricated.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    NY_Rob
  • mstarbird
    mstarbird Member Posts: 10
    The loop on the heat and hot water at 15 psi gives really low water pressure at the far end of the house. It was upped to 20 psi this summer and worked great. The 25psi started today.
  • mstarbird
    mstarbird Member Posts: 10
    To answer Ebebratt-Ed's question, yes it enters the back flow 1st then the watts then the boiler. Just doesn't sound like the water is making it through the regulator.
  • Intplm.
    Intplm. Member Posts: 2,163
    I must ask...............Is the water on? Did you remember to open (all) the manual valves supplying water to the boiler?
    I ask because it looks like from the pictures that you also have a new manifold and circulators installed. Quite a bit of work.
    Hey ! Sometimes folks forget !?

    And re-read what Ironman said about the circulators. They are installed to prematurely fail.
  • mstarbird
    mstarbird Member Posts: 10
    Nope the manafold and the Taco's are all 14 years old. The water was on. I turned it off when I inspected the watts but in the picture you can see the water valve in front of the back flow is on. The one after the regulator is on as far as it can be turned on. The Master plumber that installed the system used a manafold that too short and the Taco's can not be turned horizontally. There isn't enough room between the zones. This plumber has cause a lot of problems.
  • Jamie Hall
    Jamie Hall Member Posts: 24,648
    Any water feeder problems you have and the temperature problem are not related at all. The temperature problem may be a bad aquastat -- if you set it to 190 and the temperature still soars, that's where I'd look first.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • neilc
    neilc Member Posts: 2,803
    @intplm
    @Ironman
    on the circs,
    I understand why the motor doesn't want to be vertically "up", it traps air,
    but what would be wrong as the picture is?
    known to beat dead horses
  • Ironman
    Ironman Member Posts: 7,521
    neilc said:

    @intplm
    @Ironman
    on the circs,
    I understand why the motor doesn't want to be vertically "up", it traps air,
    but what would be wrong as the picture is?

    Debris settle to the bottom effecting the bearing.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Intplm.
  • neilc
    neilc Member Posts: 2,803
    got it
    ty
    known to beat dead horses
  • Intplm.
    Intplm. Member Posts: 2,163
    Jamie Hall is on it. Cant tell what kind of aqua stat you have from the pictures...blurry...If the aqua stat was removed during repairs and then re-installed or hit , the temp sensing bulb or line that attaches the bulb might be damaged and therefor not reading correctly.
    Cant tell from the pics if its the type I'm describing.
    Still sounds like the aqua stat.
  • mstarbird
    mstarbird Member Posts: 10
    The aquastat is a Honeywell 4006a. Aquastat was not replaced last summer. Only the tank and the regulator and the relief valve. The Aquastat has never come out of the boiler at least not since the day it was installed. The original plumber had it set to 240. It was turned down to 220 then to 210. It's now down to 180. The temp seems to be not crossing 190 today. But the wood stove is running since temps are on the negatives. The boiler hasn't had to turn on as much today.
  • Intplm.
    Intplm. Member Posts: 2,163
    You may have solved the problem then. But set it down to 190 and continue to monitor your results..
  • mstarbird
    mstarbird Member Posts: 10
    I hope so thanks everyone for the help!!!!
  • GBart
    GBart Member Posts: 746
    yeah, your high limit should never be set above 200F, ever, maybe your plumber needs glasses