What's wrong with this picture?

cabowencabowen Posts: 15Member
edited January 12 in Radiant Heating

I came across this estimator for heat loss in a home. If the max output recommended for infloor radiant is 35 btu/hr per sq ft, then it would seem that infloor radiant would not be enough to heat a home in most of the US....!!!

Comments

  • 1Matthias1Matthias Posts: 136Member
    Wowza. I've seen some bad info on the net before, but...wowza.
  • cabowencabowen Posts: 15Member
    LOL, yeah, it must be published by the heating oil industry.....

    Maybe someone can clarify something for me...when calculating square footage of a home for heat loss estimate purposes, does one use just the foot print, or add in square footage of the (heated) basement and second floor? I have seen both and would think that just the food print wouldn't sufficient...Thanks.
  • STEVEusaPASTEVEusaPA Posts: 2,720Member
    Probably not updated since the 1920's
    steve
  • GroundUpGroundUp Posts: 452Member
    Square footage of the footprint is nearly irrelevant in heat loss calculations. 1000 sq ft with 8 foot ceilings and no windows will not have the same loss as 1000 sq ft with 20 ft ceilings and 200 sq ft of glass. Each surface (wall, floor, ceiling) has its own loss whether to outdoors or to the ground below which are calculated individually and eventually the cubic footage of the entire area is added in to get to the final product
  • SteamheadSteamhead Posts: 12,731Member
    In other words, just do the freakin' heat loss calculation already!
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • GordyGordy Posts: 9,251Member
    It’s for boiler sizing only. That way you are always sure that it’s not the boilers fault. 200k boiler with 60k radiant emitter potential. :(
  • 1Matthias1Matthias Posts: 136Member

    Probably not updated since the 1920's

    I've worked on houses from 1899 that have had lower figures than this suggests. This is just silly.
  • rick in Alaskarick in Alaska Posts: 809Member
    You can tell this is from a long time ago. Alaska and Hawaii are not even on the map!!!
    Sigh.
    Rick