Powder puff test for heat exchanger?

My boss recently gave us techs a little “test kit” for checking heat exchanger integrity. It consists of a little rubber bulb filled with a very fine powder and an attached rubber tube. The idea is to have the furnace set to off with just the fan running. You squeeze a little puff of powder into each chamber entrance and if the powder blows back he wants the furnace condemned. I haven’t found any info on using this powder test anywhere online and nobody I know has used it for checking exchangers.
Any thoughts on this “test”?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    Never ran into that, but I can see how it would work: you are looking to the fan to pressurize one side of the heat exchanger, and if there is a leak that will blow out the other, where you put the powder. Not sure how sensitive it would be, though.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    What if with the unit off you're getting a little down draft or back draft? Do you block the flue and combustion air intake as well?

    Doesn't seem conclusive enough to condemn a furnace, seems more like an easy way to talk people into getting a new furnace.

    But I guess if it does blow back you should investigate further to look for a visual clue.

    I'd trust my analyzer first, then smoke candle. If any of those threw a clue, I'd do a visual.

    There was an error rendering this rich post.

    delta TSolid_Fuel_ManBlueFrostLLCGBart
  • SuperTech
    SuperTech Member Posts: 2,430
    I'm with Steve on this 100%. Sounds like an attempt to scam customers.

    I hope your boss provides you with a digital combustion analyzer so you can test the safety the equipment the proper way.

    Digital analysis or smoke pen
    GrallertSTEVEusaPAGBart
  • Grallert
    Grallert Member Posts: 774
    I've used my combustion analyzer to test for faults in heat exchangers. It seems that the O2 sensor is accurate enough to pick up any drop in oxygen levels. Also CO numbers will climb but not as clearly as the O2 level. This will prompt me to investigate further.
    Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker
  • SuperTech
    SuperTech Member Posts: 2,430
    There's nothing wrong with pulling out the blower assembly and visually inspecting the heat exchanger. A digital inspection camera makes it easier to find flaws in the heat exchanger.

    Don't ever condemn a heat exchanger unless you are positive it's shot. I've been to several houses this year that other "techs" have condemned units based on appearance of the flame or other ridiculous reasons in an attempt to sell new equipment. One idiot from another company was fired after I proved that the furnace he condemned was fine.
  • BlueFrostLLC
    BlueFrostLLC Member Posts: 3
    Yeah, I’m not feeling the powder alone process. We used to have classes with Ellis Prach for inspecting exchangers so using a mirror, camera, even water spray in my preferred way to the powder. It seems too inconsistent or inconclusive
  • Alan Welch
    Alan Welch Member Posts: 270
    If there is a heating register or humidifier mounted on the supply plenum that can be easily removed, I will to see if any light visible when the burner runs. I have found several that way.
    SuperTech
  • ratio
    ratio Member Posts: 3,790

    If there is a heating register or humidifier mounted on the supply plenum that can be easily removed, I will to see if any light visible when the burner runs. I have found several that way.

    Now that's downright scary!

    The last HX I condemned I never did find a hole, but the pressure switch would open after the HX was warm. I suppose it could have been some kind of blockage.

  • HVACNUT
    HVACNUT Member Posts: 6,332
    The analyzer is the only way to go.
    For an oil furnace I have a hand held Dwyer draft gauge. Over fire test with fan off/on. It hasn't failed me yet. Analyzer for proof.
    SuperTech
  • GBart
    GBart Member Posts: 746
    edited January 2019
    SCAM

    I had one years ago, boss sent me to check out a new customer who had another company tell her the heat x was shot, I could find nothing so I asked her what he did, she said he did a Halide Test............really? I said, just how did he do this.

    She said he had a sprayer bottle with some crystals in it and needed to get some water, he filled to a level and fired the unit up, with her watching he sprayed this through the inspection door and said "see, the fire changes color, that means you need a new furnace, the heat x is shot and very unsafe"

    I told her that was a scam and to call the state.
    SuperTech
  • JUGHNE
    JUGHNE Member Posts: 11,278


    Two of these were changed just for upgrade.
    Installed in school building in 1969..counterflow.
    Apparently had holes for a long time.
    Outdoor air connection to return duct and leaky building kept kids awake.
  • GBart
    GBart Member Posts: 746
    well then whoever was doing service hasn't checked them
  • Alan Welch
    Alan Welch Member Posts: 270
    Went on a no heat call when I first started over 30 years ago. The hole round top of Armstrong heat exchanger dropped into the firebox because of humidifier mounted on supply plenum.. Asked owner if she had noticed any smells, nope.
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    I still think that as a nogo text it's not really a scam -- but it certainly isn't going to be definitive. It will suggest that there is a potential leak -- which then absolutely has to be checked out by other means.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    GBart
  • BlueFrostLLC
    BlueFrostLLC Member Posts: 3
    I really appreciate all of these comments, I had my doubts and could find NOTHING online about using powder to test heat x condition. You all have confirmed my concerns
  • JUGHNE
    JUGHNE Member Posts: 11,278
    That school administration was saving money by having the janitor fix things after they broke. :/
    GBart