Rules of Thumb and Heating Formulas?
RayWohlfarth
Member Posts: 1,656
Howdy Wall Citizens,
I have the first draft complete on my new book on Heating Rules of Thumb and Formulas. I was wondering if you have any rules of thumb, secret calculations, or formulas you like to use and think would be beneficial to other wrench twisters like myself. The book is about 180 pages already. I never knew how much we had to know.
Thanks
Ray
I have the first draft complete on my new book on Heating Rules of Thumb and Formulas. I was wondering if you have any rules of thumb, secret calculations, or formulas you like to use and think would be beneficial to other wrench twisters like myself. The book is about 180 pages already. I never knew how much we had to know.
Thanks
Ray
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
Ray,
How about the value of 231? Cubic inches in a gallon; add a decimal point & 2.31 feet water column equals 1 psi.0 -
-
Related, but uses basics to remember it.
A cube of water 1 foot on each side weighs 62.4 pounds
Area of bottom of cube is simply = (12x 12) =144 square inches
So pressure on bottom is 62.4/144 = .4333 pounds/sq inch ( psi)
That's .433 psi /foot of depth
If using oil with a specific gravity of .7 that pressure is .7 x .4333 =0.30 psi/ft
Which means a hose of that oil 10 ft tall will make 3 psi at bottom.
(check SG, gasoline = ~.7 , think #2 oil is higher)
I did so much sonabouy design work I can't forget water weighs ~ 62.4 #/cubic foot ---- ( this is it's density)0 -
-
Interesting side note ( for teaching maybe)
0.433 psi /foot of depth .... means 1,000 ft underwater it's 433 psi
And at bottom of Mariana Trench , the deepest known point in Earth's oceans. 36,070 feet depth means pressure is ~15,600 psi
(ignores that salt water is little heavier than 62.4 #/CF fresh water)
0 -
Not hydronic but a piece of ductwork 1 square foot (12" x 12") will carry 1cfm with a velocity of 1 fpm. I use it all the time when I forget/can't find my ductulator.
fuel oil 1" of vacuum for every foot of vertical lift + .5" vacuum for every foot of horizontal run.
1000 btu/lb of steam. lbs of steam =lbs of condensate. lbs of condensate/8.33=gallons of condensate.
Air handle capacity is 400-450 cfm/ton of cooling0 -
You have the math constant for a 45 degree angle? 1.414? The plumbing pros use the math, the others hold tape measures in the air and give it their best guess0
-
A chart I keep in my cloud0
-
-
When grilling 1" thick steaks, cook 2 minutes each side for rare, 3-4 mins each side for medium-rare and 4-6 mins each side for medium.
Oh wait.
My bad.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes6 -
-
Pressure drop = Longest run in feet. Add 50%. Times .04 . This is your head in feet. Dan says figure 6 feet per 100 ft of pipe.
--------------------------------------------------------------------------------------------
Formulas used to calculate annual energy costs:
Natural Gas (BtuHr loss of House / AFUE of appliance) X (Htg Load Hrs /100,000) X .77 X Gas rate per 100 cf = cost to heat.
L. P. Gas (BtuHr loss of House / AFUE of appliance) X (Htg Load Hrs /91,500) X .77 X Gas cost per gallon = cost to heat.
Oil (BtuHr loss of House / AFUE of appliance) X (Htg Load Hrs /138,000) X .77 X Oil cost per gallon = cost to heat.
Heat Pump (BtuHr loss of House / HSPF) X (Htg Load Hrs / 1,000) X .77 X Electric rate per kWh = cost to heat.
Electric Resistance (BtuHr loss of House / 3.143) X (Htg Load Hrs / 1,000) X .77 X Electric rate per kWh = cost to heat.
Cooling Costs (BtuHr gain of House / SEER) X (Cooling Load Hrs / 1,000) X .77 X Electric rate per kWh = cost to cool
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
Kw to btu X 3.41
Heat= 8.33v (delta t)Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
Most important rules are maximum fpm for ducts and maximum fps for pipes. Flout them and you'll see.0
-
I don’t think it’s a hvac formula but here it is who am I making the bill to and will that be cash or check I believe all formulas are nil until it’s fiqured out who paying even when upfront w rates hourly charges are discussed there’s always a air of you charge to come out . Yes sir re on another note I recently thought to myself while look at a job what trade is worse off for the future fitters or tin knockers and which has more hack trunk slammer I came away more confused and realized it’s not that there hacks it’s just about the money and the lack of pride nor care they take in what they do a long lol Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements