Is Neutralized needed on condensate of nat gas DHW heater tank?
Leonard
Member Posts: 903
Condensate is pumped outside ~ 3 feet up off ground, NO neutralizer, wonder how concerned I should be about it splashing back on old cement block wall with 70 year old weak mortar in the joints.
It's a tenant installed ~ 60-80 gallons nat gas fired DHW tank in a restaurant, I assume it's a condensing type since exhaust is ~ 3 inch plastic pipe.
The condensate drains to a pump, and periodically it gives a good blast of water to the outside
It's a tenant installed ~ 60-80 gallons nat gas fired DHW tank in a restaurant, I assume it's a condensing type since exhaust is ~ 3 inch plastic pipe.
The condensate drains to a pump, and periodically it gives a good blast of water to the outside
0
Comments
-
Cold climate? If so, what’s going to prevent freezing?Steve Minnich0
-
It is a low ph fluid, it could damage any masonry it splashes on. Will it drain away when the ground freezes? It could be gallons per day pumping out.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
You could collect some of the condensate and test it with inexpensive swimming pool PH strips... or a local pool place would probably test it for free.0
-
It may not be a condensing appliance. A standard power vented gas water heater is only about 70% efficient and doesn't condense. PVC vent pipe can be used because the flue gasses are diluted with a large amount of air at the water heater lowering their temp to 140* or less.
You need to get the make and model of the water heater to see if it's condensing.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
If it is going into a pump, and discharging as the unit runs, I suspect it is condensate fro a condensing style unit.
Should run 3-4 ph, here is an example of 3 ph.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It's southern NH ....COLD ~ few days at 10-15 degs F this season already.
Soil is clay, pitched away from building, concerned about splash back, old motar and blocks are weak/cheap , not much cement in them.
Sounds like ph 3 is pretty acidic, might be a problem over years of exposure
Knew I should have posted numbers, but I assumed plastic exhaust meant condensing.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements