Is Neutralized needed on condensate of nat gas DHW heater tank?
Leonard
Leonard Member Posts: 903
edited December 2018 in Radiant Heating
Condensate is pumped outside ~ 3 feet up off ground, NO neutralizer, wonder how concerned I should be about it splashing back on old cement block wall with 70 year old weak mortar in the joints.
It's a tenant installed ~ 60-80 gallons nat gas fired DHW tank in a restaurant, I assume it's a condensing type since exhaust is ~ 3 inch plastic pipe.
The condensate drains to a pump, and periodically it gives a good blast of water to the outside
  • Steve Minnich
    Steve Minnich Member Posts: 2,895
    Cold climate? If so, what’s going to prevent freezing?
    Steve Minnich
    hot_rod Member Posts: 27,826
    It is a low ph fluid, it could damage any masonry it splashes on. Will it drain away when the ground freezes? It could be gallons per day pumping out.
  • NY_Rob
    NY_Rob Member Posts: 1,370
    You could collect some of the condensate and test it with inexpensive swimming pool PH strips... or a local pool place would probably test it for free.
  • Ironman
    Ironman Member Posts: 7,927
    It may not be a condensing appliance. A standard power vented gas water heater is only about 70% efficient and doesn't condense. PVC vent pipe can be used because the flue gasses are diluted with a large amount of air at the water heater lowering their temp to 140* or less.
    You need to get the make and model of the water heater to see if it's condensing.
    Bob Boan
    If it is going into a pump, and discharging as the unit runs, I suspect it is condensate fro a condensing style unit.
    Should run 3-4 ph, here is an example of 3 ph.
  • Leonard
    It's southern NH ....COLD ~ few days at 10-15 degs F this season already.
    Soil is clay, pitched away from building, concerned about splash back, old motar and blocks are weak/cheap , not much cement in them.
    Sounds like ph 3 is pretty acidic, might be a problem over years of exposure
    Knew I should have posted numbers, but I assumed plastic exhaust meant condensing.