Steam banging
So does it make sense to take them out to clean ? Do I need to check for anything specific ? ie rust use some kinda of cleaning conditioner ? I never work with these before but willing to learn and figure out the pipe banging issue. Also does not look like there is any pitch.. so I think that might be one issue. Ill post some pics a bit later.
Comments
-
and pictures of the boiler, from the floor to the ceiling,
what pressure are you running at?known to beat dead horses0 -
Welcome to the steam fun! You’re in good hands with the folks on this forum. I was in your shoes a few months ago, except for wanting to clean stuff!
What is it that you want to take out to clean? What is “them”?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
his radiators or convectors are cakedknown to beat dead horses0
-
Internally or just outside?0
-
I wuz guessingknown to beat dead horses0
-
Pictures of your radiators or convectors also will be helpful.0
-
Cleaning radiator or convectors won't stop the banging. If we are talking about a steam system, something is holding water. Either the radiator/convector is pitched the wrong way or a pipe is incorrectly pitched or has a bow in it holding water. As the others have said, post some pictures,; the boiler, the piping above it, and a representative sample of the radiators/convectors. If you can isolate where the banging occurs, that will help a lot.-1
-
Sorry, I had flu and didn't get out of bed till today, nasty 5 days. I will try to take pics, it looks like non of them are pitched. Theres only 1 pipe in and the basement is sealed. Im hoping to crack some sheet rocks open to figure out whats going on.
Outside is nasty, painted over, a few times, i m sure inside is nasty too.. lol.0 -
Don't trust your eye, use a level to confirm pitch or no pitch. Try stretching a string along long runs of pipe to check for dips in the piping.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Sorry for the delays.. Ill get some better photos. So it looks like these are 1 pipe system ? it goes in and does not go out
They were painted over and was falling off, I have 2 yr old but didn't want him to start eating paint chips.. My contracted had strip some off but was going to paint them in spring. I was wondering if I can just take the whole thing out and pressure wash them. I put new vents on them. The boiler people said they could have been pretty old.
Banging
https://youtu.be/x1NBKpDwGdQ
More banging
https://youtu.be/Pk4max0td8U
https://youtu.be/-fdeAcyEhiw
It might be hard to hear with the vent going off. Ill take pic of the pipes. Its just one pipe in and get a level to look at the pitch. I'm pretty sure its just flat on the floor
The boiler is a Weils EG/PEG50
let me know what other info I should get0 -
Last but not least, all the pipe are in the floor which are all closed off and finished. So I am debating to open them and refinish them if it can be fixed. Else no use opening all the finish work and not do anything0
-
Unfortunately it sounds like you may have a sagging pipe but first make sure your radiators are pitched to drain towards the floor valve which is located behind the lower grate. It is not easy to do with built in Sunrads.
Do you ever hear a boiling sound during your heating cycle?0 -
Don't open the floors. First, make sure the hammer is actually at those radiators and not just radiating from the main up to those radiators. Are all of the banging radiators on the same main in the basement? If so, see if the hammering is louder along that mai and if there is a sag (bow) in that main that is holding water or if a hanger has come loose and allowed the main to drop a little and changed the pitch.
If the noise is actually at the radiators, make sure the radiators are pitched back towards the supply valve.
If you find the radiators are properly pitched and the noise seems to be coming from below the floor boards, try to raise the supply side about a half inch and the repitch the radiator. Raising the supply side of the radiator will also raise any horizontal pipe under the floor that may have lost its pitch.-1 -
-
-
He's got Hoffman 1A's on there. They can be adjusted to a setting of "2" and be equal to the Gorton #4. At "1" they are even slower.gfrbrookline said:Also what are your Hoffman vents set at? I found that putting Gorton #4's on made a huge difference. These are small radiators and like to be vented very slowly.
0 -
-
I don't know what size supply pipes he has (pictures would be good) but if they are 1.25" or better and his system pressure is where it belongs, he is not likely to get banging from venting too fast. Spitting, maybe, heating across the top or bottom half only, possibly but not likely banging. Something is most likely out of pitch.gfrbrookline said:That is why I was asking, if they are set to anything above 2 they are venting too fast and condensing faster than they can drain on initial heat up so that is likely the clanging he hears.
-1 -
Ill have to provide some info in the next few days. But the hoffman are set between 2-5, farthest one is at 5, ill try to make a drawing, its hard to tell where its banging, sounds like the pipes, not the actual radiators, sounds like right below the radiator..0
-
Ok heres some banging sound.. Originally I thought it was mostly pipes but looks like something is wrong with the boiler.. it sounds like its coming from the damper or that white box by damper.
https://www.youtube.com/watch?v=iZ2sBS8uNDk
Damper is GVD-7
So originally the furthest 2 radiator was set to 4-5, lol. I drop all of them to 1, should it be 1 ? Its a small house, 40x100 lot, so house is like 20x50 or something.. not huge. Can you set them to lower than 1 or 1 minimum. They moved as I tighten the top so may have gone toward less than 1
0 -
This pic of pipe is in garage. It’s the furthest point in front of house. The boiler is at opposite end of house. So that little round thing in too blows out steam or something. And water leaks out sometimes. Not sure what it’s call
BTW is the damper suppose to open and close or only at certain times.. thanks.0 -
Where are you located @LeSer?0
-
Unfortunately the boiler needs to be repiped, it appears to be an EG50 which according to the Weil-McLain manual should be a minimum of one 2-1/2 riser and header, what you have appears to be 2”, and it isn’t configured properly. Also an EDR needs to be done on the radiators to see if the boiler is sized correctly.
What your hearing is what Dan Holohan refers to as the anvil chorus aka water hammer usually created by wet steam over sizing or improper piping.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
I am in nycDanny Scully said:
Where are you located @LeSer?
0 -
Yes its a EG/PEG-50. The boiler was replace by previous owner before we move in. Not sure if he got the cheapest quote or something. It was part of an oil to gas conversion.Dave0176 said:Unfortunately the boiler needs to be repiped, it appears to be an EG50 which according to the Weil-McLain manual should be a minimum of one 2-1/2 riser and header, what you have appears to be 2”, and it isn’t configured properly. Also an EDR needs to be done on the radiators to see if the boiler is sized correctly.
What your hearing is what Dan Holohan refers to as the anvil chorus aka water hammer usually created by wet steam over sizing or improper piping.
Ill give it a measure, 2.5 is diameter ?0 -
@LeSer yes MINIMUM size is supposed to be 2.5” we as usual always go bigger as it works much better. Here is a chart of the outside pipe diameters which will give you the nonminal inside diameter.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......-1 -
What do you think repiping will cost, is it just the area mention in the manual ? you're in neighbor state, so price should be almost similar.. or what would you charge, so I can find out from previous owner if he can get these yahoos to fix it0
-
We don’t talk cost, and money here, so you will just have to tell them that the installer they chose did not follow the instructions, which came with the boiler and that it is now not properly functional.
It would not have cost that much more to do it right from the beginning. I think you have a good case against them if it comes to a lawsuit.—NBC-1 -
What we can see of your steam main pipe is running up hill away from the boiler. That is a counterflow pipe in that steam is try to flow against returning water. If not handled correctly this will product water hammer.
If much of your horizontal steam main piping is sloped as such then that calls for different piping at the boiler.
That piece of sheetrock that is only screwed on the wall could be removed to show more of the piping.0 -
All of those strict codes in NYC and still steamers get piped completely wrong.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@LeSer you said you’re in NYC but that looks like a Brooklyn/Queens basement to me. Dave0176 is top notch and you should follow his lead if he’s offering, but if he’s too busy, I’m able to guide this to resolution.
Best to all,
JCContact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
I noticed that too @JUGHNE that main is pitched pretty good towards the boiler. If it is indeed a counterflow, that could explain the major water hammer in the header area.JUGHNE said:What we can see of your steam main pipe is running up hill away from the boiler. That is a counterflow pipe in that steam is try to flow against returning water. If not handled correctly this will product water hammer.
If much of your horizontal steam main piping is sloped as such then that calls for different piping at the boiler.
That piece of sheetrock that is only screwed on the wall could be removed to show more of the piping.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
There look to be wet/dry returns also.
Maybe it is a hybrid.
Counter flow to get height in maybe the crawl space or avoid a beam we don't see and then switches to parallel flow0 -
Hi, What is hybrid. Is it steam and radiant ? basement appears to be radiant, water pipes.. hybrid ?0
-
His reference suggests the possibility that the steam main may start out pitched towards the boiler with a drip, near the boiler and then at some point that same main starts to pitch the other direction, with a drop into a wet return at the end of the main. This is sometimes done to get the main past a spot where headroom is restricted but the main still needs to move condensate back to the boiler without it pooling somewhere along the way.LeSer said:Hi, What is hybrid. Is it steam and radiant ? basement appears to be radiant, water pipes.. hybrid ?
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements