steam boiler sizing
dobro23
Member Posts: 71
Here's an easy one. quoting a steam boiler replacement where the load is 211 EDR. the boiler also has a hot water baseboard loop off the main vessel. not a coil or other heat exchanger. the baseboard is 18000 BTU. how does this get figured into the equation? what size boiler will handle this combined load or do i only size for the 211 EDR?
0
Comments
-
Size for the EDR. That has a pickup factor built into it (at an EDR of 211, it would around 60,000 BTUh). In the unlikely possibility that both the hydro zone and the steam system are calling together, the pickup will be ample to feed the system. If they both start exactly together (even less likely!) all that would happen is the boiler would come up to steam a little slower.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England-1 -
What @Jamie Hall said
Hot water load cannot exceed your pick up factor which yours does not so your good.-1 -
> @dobro23 said:
> Here's an easy one. quoting a steam boiler replacement where the load is 211 EDR. the boiler also has a hot water baseboard loop off the main vessel. not a coil or other heat exchanger. the baseboard is 18000 BTU. how does this get figured into the equation? what size boiler will handle this combined load or do i only size for the 211 EDR?
You only size for the 211 EDR, do not add extra for the hot water loop.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......-1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements