Monoflow mess

Wayne55
Member Posts: 10
I inherited this, one boiler wasn't doing job someone added other boiler.. basically 3 zones ( 3 circulators) can someone tell me how I can put the pics. From my phone on here please ..be easier to show then ask my wuestion.been out of commission for about 5 yrs.
0
Comments
-
Figured how to get pics. 3 floors,3 circs,seems 2nd and 3rd on one boiler,1st floor. On other boiler.but suppy and return are twin together .1st floor. Circulator seems to be pulling h/w from 2nd and 3rd floor.boiler.would it make sense to put check valve on return side so it can't pull h/w from boiler0
-
Your pics need to be from farther back showing as much of the piping as possible.
The Grundfos circulator needs to be mounted completely horizontal, not half way vertical.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I cannot make any sense of it but does anyone find it funny that a Hot Water system is piped in Black Iron. If only some of the new steam installers could do that instead of copper0
-
^It's probably because it's originally piped in black iron.0
-
It was originally piped in blk. Iron. I will get better pictures tomorrow. I was going to take that 1 inch line out put circulator completely on horizontal when I got call mother got rushed to hospital so I just slapped it in. I appreciate the feedback hopefully tomorrow I get better pics explain this mess better and I get some more feedback..thank you guys0
-
Hope these pics are better,couldn't move back any further . Ok there's 3 circs,3 relays,and 2 aquastats.whats happening is 3 floors,turn heat on 1 St floor and radiators on 3rd floor getting hot ..it's a monoflow system .if these two boilers are connected what would prevent 1st floor. Grundfos coming on and pulling return water from other 2 zones0
-
Again I appreciate the feedback... This is pretty much volunteer work, it's a club for friends of bill w0
-
That's messed up. Can you draw out the boiler piping layout.0
-
Just a heads up,I got run over my truck 4-5 yrs. Ago.screwed up my motor skills a little.cant draw straight.2 boilers tied together a off the main there's a 2x1 tee tieing into return.monoflow system,so I turn heat on 1st floor it's getting radiators hot on 2nd and 3rd floor .all circulators tie into return line not into boiler separately any suggestions0
-
Any suggestions guys besides find a new trade lmao.0
-
-
You can keep the two boilers considering that they are already there. Just not the way its piped now! I'd also re-do the entire near boiler piping, pump away. I'd consider giving each boiler it's own pump and pipe it primarily/secondary. That way you can lead lag the boilers and have total redundancy for just the cost of two pumps.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 943 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements