Steamer and steam main repipe
EzzyT
EzzyT Member Posts: 1,379
The steam mains, main venting and wet return flushing valves we did a couple of week ago.
The steamer repipe we did today.
Still have to go back to skim some more and wand the hell out to the boiler and flush the wet return.
Also have to down fire the boiler by replacing the burner tray assembly since the boiler can be used with two different fire ratings, and the homeowner now wants to install s automatic water feeder.
Didn’t have any DM filters in stock still waiting for more to come in. Installed a CO detector with a relay that will kill the boiler if the CO detector alarm goes off
E-Travis Mechanical LLC
Etravismechanical@gmail.com
201-887-8856
ethicalpauladasilva
  • clammy
    clammy Member Posts: 3,256
    Great looking job ezzy You cranking it out keep up the great work your a true credit to the craft of steam fitting a true sight for tried eyes. Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,593
    That might be one of the last Williamsons piped using two tappings. 😥
  • LionA29
    LionA29 Member Posts: 254
    Awesome install @EzzyT