Roth Tank
RonDuch
RonDuch Member Posts: 3
Is there a problem with a Roth Tank? I have a Roth tank 1000 with a oil fired boiler nad an oil fired hot water heater connect. The both systems can run for about 3 days and then the one closes to the tank gets air bound and it has to be bled. The one further from the tank never gets air bound. I tried tlocate the problem and when I thought I found it it comes in for service and the pump has to be bled. Is there a problem with connecting two heating unit to a roth tank?
    Jamie Hall Member Posts: 27,232
    Shouldn't be. Sounds like an air leak in the line that gets air bound.
    STEVEusaPA
  • Grallert
    Grallert Member Posts: 1,105
    Does the tank have the original rubber suction line in it? That component was often a problem it could collapse under suction or crack at the top connection.
  • Vt-techAL
    Vt-techAL Member Posts: 1
    There should be a 2 line system to both units or a de-aerator according to Roth. We've had problems with air bound systems also. Connections were tight and leak free in all but still got air bound. Went back and installed a Tiger Loop on every one and never had a problem since. We install a Tiger Loop on every Roth install now. Not pitching for them but that's what we use vs 2 line system
    rwhtg