    Dan,

    Excellent work and read.

    Although i would point out that i would have left the steam traps out of the equation here since you now have a wet return with very low pressure. What type of steam traps did you specifically utilize? Mechanical or thermostatic? i would be hesitant to add steam traps to the system as the original did not have them and operated at a very low pressure as you stated. With this low pressure the banging noise would have been eliminated anyways dont you agree.

    excellent retrofit.

    thanks for the article.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,477
    nice job!!
  • 33445delray
    33445delray Member Posts: 1
    Nice read. By lowering the return to the floor you created a Hartford Loop.
  • dopey27177
    dopey27177 Member Posts: 887
    Knowledge and common sense made the pathway to selling the job to the customer, by restoring the system to an operational state even with the new boiler you saved the customer a lot of money over time,

    Jake
  • jumper
    jumper Member Posts: 2,385
    Correctly designed steam with dry return and trapless radiators excels. Correct design requires condensate gets back into boiler and air is expelled somehow somewhere.
  • JUGHNE
    JUGHNE Member Posts: 11,276
    edited September 2021
    Excellent observations and repairs, very good work.

    When you did the EDR calculations for boiler sizing, did you downsize by 20% for the oversized radiation?

    And was there a reason to not put orifices in the new supply valves and not add traps?