Btu question

keith_27
keith_27 Member Posts: 64
edited November 2018 in Domestic Hot Water
what is the btu for bare 3/4 copper in the basement

Comments

  • Ironman
    Ironman Member Posts: 7,516
    That depends upon the temp differential between the pipe and the ambient air. At 70* ambient air and 180* in the pipe, it's 45 btus per lineal foot.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Gordy
  • hot_rod
    hot_rod Member Posts: 23,127
    flow rate inside the pipe as well as any air movement around it will have some effect. Keep in mind the temperature drop, measure SWT and RWT, add those two then ÷ by 2 to get average temperature across the run. Use that average for your estimates.
    Bob "hot rod" Rohr