Installing a Nest Thermostat for heating with an ARGO 6P Zone controller
gjlian
Member Posts: 4
Replacing a Honeywell 2 wire thermostat with a Nest "Smart" thermostat is causing chattering of the relays. I've been reading forums and called both Nest as well as ARGO for advice. Nest simply told me to run a 3rd wire to the common terminal on the Nest which is a major hassle in an old house. I've also read about installing a local 24 volt power source near the Nest thermostat which is clunky in my opinion. Any thoughts or ideas are welcome. Thanks
0
Comments
-
I had to pull new t-stat cables when I when from old 2-wire stats to modern programmable stats. It was a pain pulling new wires, but better than running a wall-wart transformer to each t-stat for power.
You can temporarily run any of the new stats off local 24vac transformers till you can pull new cables back to your boiler.
Ironically... when I upgraded to a mod-con boiler, I went back to simple 2-wire t-stats again0 -
As @NY_Rob says -- take your pick. Or pick one of the battery powered, programmable Honeywells, if you don't need internet connectivity.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Or get an Add a Wire kit. I think Ecobee includes that kit with some of there stats.
https://smartthermostatguide.com/c-wire-venstar-add-a-wire-adapter-review/Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
@hot rod ....
I looked it to that "add a wire kit" and stopped where it stated "Cannot be used as "R" power or "C" common wire. "
If you look at the Q&A on Amazon it states:
"Unfortunately this cannot be used to turn 2 wires into 3. It is specifically designed for 4-5 or 5-6 situations."0 -
Thanks for all the posts. I'm planning on installing an ARGO IR 882 (isolation relay) alongside the ARGO 6P this weekend. I'm told this will solve the problem. Total cost - $65 for IR 882 + $20 for 120/24 v transformer needed to power the relay. I will post the results on Monday in case anyone is interested.0
-
^ Will the ARGO IR 882 supply power needed for your Nest over the existing 2 wires? I would contact them to be sure.0
-
Good to know, someone suggested there is a kit that can add a common. Maybe wi fi? Is that what Ecobee uses?NY_Rob said:@hot rod ....
I looked it to that "add a wire kit" and stopped where it stated "Cannot be used as "R" power or "C" common wire. "
If you look at the Q&A on Amazon it states:
"Unfortunately this cannot be used to turn 2 wires into 3. It is specifically designed for 4-5 or 5-6 situations."
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I did speak to ARGO and yes they said it should work. I have a back up plan in case it doesn't but I'm cautiously optimistic at this point.0
-
I hope you will post back with results.....0
-
-
Gjlian, I have the same issue. Can you post a photo of the final wiring at the argo boards?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements