Legitimate Reasons to Raise Steam Pressure

I know that oftentimes on steam boilers, people will unnecessarily raise steam pressure to compensate for system deficiencies when there is really another issue that needs to be addressed.

What I'm wondering is, what are some actual, legitimate reasons that one would need to raise boiler pressure?

Thanks in advance, sorry for a novice question.

Comments

  • Jamie HallJamie Hall Posts: 8,961Member
    Assuming that we are talking heating systems here, and not process steam or power -- the first one that comes to my mind is that certain types of heating coils or reheat coils in air handlers do require a higher pressure sometimes.

    I'm sure @Steamhead can come up with some more.
    Jamie



    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.



    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • RayWohlfarthRayWohlfarth Posts: 533Member
    I have seeen higher steam pressures on steam to water heat exchangers, typ 5-7 Psig
    Ray Wohlfarth
    Boiler Lessons
    Click here to take Ray's class.
    Click here to buy Ray's books.
  • ChrisJChrisJ Posts: 9,196Member
    Legitimate reasons to raise steam pressure?

    I suppose if you want to get into New York early Tuesday night and make headlines......
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Phil53Phil53 Posts: 52Member
    Smaller distribution piping - like Gerry's mini tube?
  • gerry gillgerry gill Posts: 2,872Member
    To raise condensate to a higher level than the trap discharge level.
    gwgillplumbingandheating.com

    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • HVACNUTHVACNUT Posts: 1,597Member
    Dry cleaners use high pressure.
    Fulton downfire 90 psi
  • EBEBRATT-EdEBEBRATT-Ed Posts: 4,512Member
    As already mentioned, air handler coils, heat exchangers, high temperature requirements, lifting condensate, steam humidification

    I