Indirect with an HTP UFT boiler
GroundUp
Member Posts: 2,124
Anyone partner these two? Not specific to the HTP indirect necessarily, but I'm having a hard time figuring out how to set the DHW temp separately from the CH output temp. I'll be honest, this will be my first indirect with these boilers so I may very well be missing something obvious. At the present time I don't physically have an indirect in place, but do have a UFT-80W in place heating a 2500 sq ft slab. The second zone circ was added for future DHW zone at original install. ODR sensor is giving me 104 degree CH water, so where can I change that to 140 output for the indirect? I've read the manual both ways 15 times and have only managed to muster a headache. Do the SuperStor tanks signal the boiler what temp to run?
0
Comments
-
-
Wire the circulator to the DHW terminal in the boiler. Wire the tank sensor to the boiler. Configure as needed...."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Uh huh, circ turns on and runs 104 degree water through the coil for 100 years trying to reach 140. It never comes. I'm asking how to change the DHW setpoint in the boiler, because the manual does not give that information nor can I figure it out by navigating the system on my own. There is no DHW anything within the settings that I can find0
-
If it's a SuperStor indirect, it has a thermostat like an electric water heater. Just wire that back to the domestic low voltage terminals and the pump to the domestic high voltage terminals.
The control comes set to look for an aquastat, but can be programmed to use a tank sensor.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.-1 -
If you pipe it per the manual and set it up for domestic priority, the controls will do the rest"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Let's say it's not a SS tank and only utilizes a mechanical aquastat. The rise/fall of the aquastat are only going to signal the pump when to run, right? "Domestic Priority" is nowhere to be found- so for a third time I will ask HOW do I find these domestic settings? There is nothing in the manual, nor can I find anything in the settings
0 -
I believe you will need an EXP relay that has an isolated end switch and a priority to go from the DHW zone to the boiler DHW contacts. Other wise the boiler will try to make hot water at too low a temp.0
-
I think you are over thinking this....
Wire the circ where it says DHW circ. You will need the other zone circ to be wired to CH circ so it will turn off with DHW call. Wire the sensor or aquastat to the DHW sensor terminal. I would suggest pulling whatever comes with the tank and using the HTP sensor in it's place.
Configure it using this section of the manual.
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein-1 -
IDK why your getting so worked up at folks who are trying to help you. Everything that you keep asking for IS in the manual.
Display parameter 39 is used to tell the boiler if you're using an aquastat or a sensor.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
In the current Install manual, page 55: item 25ST in the installer menu sets the boiler supply water temp sent to the indirect.GroundUp said:Anyone partner these two? Not specific to the HTP indirect necessarily, but I'm having a hard time figuring out how to set the DHW temp separately from the CH output temp.
If you want to set the indirect DHW temp higher or lower than the factory default of 120F, that's item 21:dh in the installer menu.
-1 -
FWIW- I have the UFT-80W and a SSU30 indirect using a sensor.
Early on I had a flow-check go bad and since my t-stats control the zone valves directly- they were still open on DHW calls which lead to ghost flow on DHW calls. My indirect was taking forever to heat up to 135F till I noticed the ghost flow condition and replaced the faulty flow-check valve.
Check your spaceheating loops during DHW calls (just put your hand on the supply pipes)... you should not feel increasing temps in them during a DHW call.0 -
Worked up? Nah. But I did have to ask the same question 3 times to get an answer that was as simple as "there is a way to change it in the manual". Now, it turns out that the manual I got with this particular unit is missing 14 pages somehow. I pulled another one from a new unit on my shelf and found what is posted above, so thanks all for helping me find that I was missing pages. I spent 2 hours this evening trying to navigate my way through the settings to get there and cannot, so I'm going to scrap the idea until I haven't been awake for 30 hours and I have a little bit of brain activity. I appreciate the help fellasIronman said:IDK why your getting so worked up at folks who are trying to help you. Everything that you keep asking for IS in the manual.
Display parameter 39 is used to tell the boiler if you're using an aquastat or a sensor.0 -
you can find a you tube video for most everything these days. Nice thing about them is you can stop, rewind and play again to help grasp the concept.
I searched HTP boiler control, here is a link to several dozen videos, not sure which model you have.
https://www.youtube.com/results?search_query=tube+HTP+boiler+control+program&page=1&utm_source=opensearchBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I had already done the same and there is nothing about the UFT control unfortunately. I will just call HTP when I'm standing in front of it next week, I don't have 20 hours to waste trying to figure it out on my ownhot rod said:you can find a you tube video for most everything these days. Nice thing about them is you can stop, rewind and play again to help grasp the concept.
I searched HTP boiler control, here is a link to several dozen videos, not sure which model you have.
https://www.youtube.com/results?search_query=tube+HTP+boiler+control+program&page=1&utm_source=opensearch
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements