large residential oil furnace needed
zepfan
Member Posts: 408
in Oil Heating
We are looking at a job which is a complete system replacement, the house has a 200 mbh 1972 oil furnace, and five tons of ac. The house is about 5,000 ft. 2 and I am sure if it was built today they would have had two systems. While the furnace may have been too large from day one, the issue is I can't seem to find anything close to the size of this made now. I am seeing most furnaces topping out at around 132 mbh. Any assistance would be much appreciated. Thanks to all.
0
Comments
-
-
The Weil-McClain 380 comes in at 209 net MBtuH for steam. The n80 series goes up from there. Cedric is a 580 firing at 2.75 gallons per hour, for instance. Check your EDR, though!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
Heat loss calculation is needed.To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
Isn't the poster asking about forced air?Jamie Hall said:The Weil-McClain 380 comes in at 209 net MBtuH for steam. The n80 series goes up from there. Cedric is a 580 firing at 2.75 gallons per hour, for instance. Check your EDR, though!
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
Stupid assumption on my part. Maybe he is; not clear. Where's my coffee?JohnNY said:
Isn't the poster asking about forced air?Jamie Hall said:The Weil-McClain 380 comes in at 209 net MBtuH for steam. The n80 series goes up from there. Cedric is a 580 firing at 2.75 gallons per hour, for instance. Check your EDR, though!
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Thanks to all for responding. Yes this is a forced air furnace with five tons of central ac0
-
-
Adams manufacturing in Cleveland makes them up to 1,000,000 btu.0
-
As stated above it is 2018, you have to do a heat load calc, you can't pull a permit without, THEN you pick the equipment, I wouldn't be surprised if your actual load was @ 125,000btu/hr.0
-
I echo the above. Please do a heat load calculation for your own education.
Slantfin has an app. It is tedious but worthwhile.
I had an oil company contractor walk in and quote a 225,000 BTUH, input, oil furnace when a 112,000 BTUH, input, would do. Think of all the oil we would have had to buy for that beast for years and years!1 -
What is sad is that today many times contractors do have a load calc to give the inspector and they do miraculously match the output of the unit but they are a complete FRAUD.
Or the contractor tells the supply house "yeah its like a 30 x 45 house with a um 8ft ceiling and 2 bedrooms, I think the side walls are 20, yeah" and they design build off that0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements