Radiator Venting
gfrbrookline
Member Posts: 753
I have a one pipe parallel steam beating system in a Boston row house condo building. Most of the radiators are vented with Hoffman 40's with a few Ventrite #1's in cold rooms and the heat is even in all but my top floor unit, who is complaining it is too hot in her unit. She is claiming it is 104 while the rest of the building is 68 to 70 in the winter, no set backs. She will not let me put anything in her unit to confirm her findings so am suspect. Would there be anything wrong with putting Gordon #4's on large radiators on the top floor, it kind of puts their chart up side down. When I say large they are the same five and six fin radiators as are in the two units below.
She used to have Honeywell TRV's on the radiators which she turned off during the day and on at night, coutner intuitive right. That made the boiler short cycle during the day and pipes bang at night since it didn't have a vacuum breaker. Since I put the 40's on both issues have stopped. I am guessing she want to have independent control of her heat back and the 104 is bogus since I can't imagine there could be a 30 degree difference with the same edr one floor up.
She used to have Honeywell TRV's on the radiators which she turned off during the day and on at night, coutner intuitive right. That made the boiler short cycle during the day and pipes bang at night since it didn't have a vacuum breaker. Since I put the 40's on both issues have stopped. I am guessing she want to have independent control of her heat back and the 104 is bogus since I can't imagine there could be a 30 degree difference with the same edr one floor up.
0
Comments
-
TR vents shouldn't cause hammering. TR valves will surely do so. Which were they?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Sorry, they were valves.0
-
honeywell V2042HSL10 to be exact.0
-
Those should not have caused hammering, as although they are called valves (thanks, Honeywell) they are -- or should have been -- mounted as and used as vents.
Always assuming that the radiator inlet valves were fully open at all times...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Regardless of what they are called when they were replaced with Hoffman 40's all things went quiet.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements