Bosch Greenstar
Options
Harvey Ramer
Member Posts: 2,281
With the crc100 control, do you also need ODR?
0
Comments
-
-
No, it uses the indoor temp only. It raises or lowers the water temp based on the temp difference between the room setpoint and the actual room temperature. It is a constant circulation control. With the CRC 200, it uses the outdoor sensor ONLY for warm weather shut down. That feature isn't in the CRC 100.1
-
> @Noel said:
> No, it uses the indoor temp only. It raises or lowers the water temp based on the temp difference between the room setpoint and the actual room temperature. It is a constant circulation control. With the CRC 200, it uses the outdoor sensor ONLY for warm weather shut down. That feature isn't in the CRC 100.
Thanks! I was thinking that's the case but I couldn't find any difinitive information.
Indoor reset rocks on a single zone system. It's better than outdoor reset in that application.2
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements