Armored wiring for a 24 VAC system

EdwinD
EdwinD Member Posts: 159
I'm configuring a Pressuretrol and Vaporstat for a 24 VAC system steam boiler.

Can I use aluminum armored wiring for a 24 VAC system? If so, what size?

Thanks
Weil-McLain EG55 2 pipe Vapor System
OP Pressure .10 -.25 oz
8-Way Boiler Water Treatment
Barnes & Jones Big Mouth Vents

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    Frankly, I wouldn't use aluminium wire for anything -- 24 vac or no. Use copper wire.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    1MatthiasEdwinD
  • ratio
    ratio Member Posts: 3,790
    I think @EdwinD means Al jacketed MC or possibly Al FMC with Cu conductors? In which case local codes might say otherwise, but other than that should be just fine. #14/2 MC is good for 15A under most conditions, a 40 VA xfrmr is good for nearly 2A; way overkill but not too hard to come by. #16 TFFN in 3/8" flex would look nearly the same but probably cost more in the end, accounting for the labor spent in sourcing it. Normal stat wire in 1/2" flex could be done from a Big Box store and might be the cheapest way to get it done.
    EdwinD
  • EdwinD
    EdwinD Member Posts: 159
    @ratio @Jamie Hall Correct, jacketed is what I want. I'll go with Normal stat wire in 1/2" flex. Thanks!
    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • HVACNUT
    HVACNUT Member Posts: 6,332
    If you're referring to Greenfield aluminum flexible conduit, that's fine. You can sleeve regular thermostat wire or THHN through it.
    You just can't sleeve 24v low volt thermostat wire in the same conduit with line volt unless they are of the same gauge, usually #14 or larger.
    EdwinD
  • EdwinD
    EdwinD Member Posts: 159
    @HVACNUT Thanks! I want wire already sleeved, so I guess Greenfield aluminum flexible conduit is what I need? Whats the smallest size I can use?
    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • ratio
    ratio Member Posts: 3,790
    Flex is empty, you have to add the wires you need. MC cable has a number of conductors in it, most common is #12 gauge solid, but it is available with #14, and stranded, conductors; likely a special order at an electrical supply house. You probably don't really want to use MC cable.
    EdwinD
  • HVACNUT
    HVACNUT Member Posts: 6,332
    edited June 2018
    Greenfield with wires already sleeved is called B/X. Residential is usually 3/8" clad. You can get up to 4 conductors with #14 wire.
    14/2, 14/2 with ground wire, 14/3, 14/3 with ground, etc.
    Use 1/2" straight or 90° angle connectors.
    The big box stores have it packaged to length. 25'- 50' etc.
    Also invest in a B/X cutter and buy a bag of "Red Heads" insulators so the metal doesn't cut into the wires.
    EdwinD
  • EdwinD
    EdwinD Member Posts: 159
    Fantastic. You guys are really helpful! I'll mull my options. Thanks!
    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,479
    @EdwinD

    I would recommend 3/8" or 1/2" flex either made of steel or aluminum. If it is aluminum you must use a "squeeze" type connector that won't damage the aluminum jacket. You can use straight or angle connectors or 45 deg connectors. It's better to use stranded connectors with crimp on sta kons. It's just a better job than solid wire.
    EdwinD
  • EdwinD
    EdwinD Member Posts: 159
    @EBEBRATT-Ed Got it! Thanks for your input! Stranded connectors with crimp on is what I prefer. All appreciated.
    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • Steamhead
    Steamhead Member Posts: 17,384
    HVACNUT said:

    If you're referring to Greenfield aluminum flexible conduit, that's fine. You can sleeve regular thermostat wire or THHN through it.

    You just can't sleeve 24v low volt thermostat wire in the same conduit with line volt unless they are of the same gauge, usually #14 or larger.

    Actually, IIRC all the wire in this type of installation has to be insulated for the maximum voltage that will be encountered therein. In this case that would be 120 volts. So, even the wire carrying 24 volts must have insulation rated for at least 120 volts.

    Ordinary circuit wire, as found in Romex or MC (formerly BX) cables as well as conduit installations, is rated for 600 volts. That's more than enough. However, I don't think the usual thermostat wire is rated for much more than 50 volts. If that's true, you can't put it in the same conduit or flex as 120-volt wiring.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    EdwinD
  • JUGHNE
    JUGHNE Member Posts: 11,276
    Whatever wire you use, stranded #14 with crimp connections is the most user friendly now and in the future when pigtails have to be removed. Solid wire puts some strain on the small control screws.

    Steamhead, years ago I was called on running 24 volts in raceway with 240 volts. All insulation was rated for the nominal 600 volts. The issue was the class of transformer providing the 24 VAC. IIRC there are 3 classes. The class is determined by the over current protection for the transformer.
    I guess the scenario could be insulation failure of both circuits inside the raceway. Feedback thru the transformer could cook the other controls in the air handler/furnace.
    That is why we have that too small of a JB in outside equipment for the t-stat wire to splice. Apparently equipment manf. are allowed the distance to the compressor contactor.

    Anyhow, since the red tag call I have always kept the voltages in separate raceways. (easier than studying the NEC book).
    Also, there may be more than one disconnect for the sources.
    Digging into a J-box when you are sure it is only 24 volts can produce some unique notches in your tools.
    EdwinD
  • Steamhead
    Steamhead Member Posts: 17,384
    That may have been a local thing. Inspectors here are OK with it.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EdwinD
    EdwinD Member Posts: 159
    @HVACNUT @Steamhead @JUGHNE @ratio @EBEBRATT-Ed @Jamie Hall

    Aluminum Cable Thhn 14 Ga (see link), is what I'm considering. I wasn't intending to sleeve wiring thru a conduit.

    I'd like to pigtail existing wiring which currently doesn't travel very far (it's attached to existing Pressuretrol at the front side of unit) then pigtail to the aluminum cable and run further back to where I'm installing 1st to Probe LWCO, then travel to top back side of case, then wire Vaporstat and then to the new Pressuretrol
    see attachement - blue line represents run of cable. I'll be removing the manual LWCO and old pressuretrol device

    Does that make sense? Thoughts?

    https://www.amazon.com/gp/product/B000BQUQLQ/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1


    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    That ought to work -- just make sure that everything is properly wired in series! Also, though it doesn't affect function, the neater you can run the wiring the happier you will be...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    EdwinD
  • EdwinD
    EdwinD Member Posts: 159
    Thanks @JamieHall
    I totally agree about the neatness factor. I want to get it in tip top shape. I'll circle back to share how it all turned out with pics and such. Waiting on parts.

    Thanks everyone!
    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • JUGHNE
    JUGHNE Member Posts: 11,276
    If you are doing some type of flex, I have found it simpler to mount a 4" square box on the boiler jacket and send a single flex to each device. Some controls have only a single knockout and room for 2 wires.
    I use 3/8" flex conduit and run the 14 GA stranded wire inside and loop thru the J-box up to the next control, etc. Fewer splices make for easier wiring and troubleshooting.
    ratioEdwinDTinman
  • EdwinD
    EdwinD Member Posts: 159
    @JUGHNE Great advice. I was thinking along those same lines. Thanks!
    JUGHNE said:

    If you are doing some type of flex, I have found it simpler to mount a 4" square box on the boiler jacket and send a single flex to each device. Some controls have only a single knockout and room for 2 wires.
    I use 3/8" flex conduit and run the 14 GA stranded wire inside and loop thru the J-box up to the next control, etc. Fewer splices make for easier wiring and troubleshooting.

    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,479
    @JUGHNE That 24 volt thing in the same raceway with 120-600 I don't see an issue as long as all the wire is 600 volt.

    But your right.

    I have never understood article 800 or whatever it is nor have I ever had anyone be able to explain it to me successfully what the problem is. Maybe I am just dumb. But @Steamhead is right it depends on location as to how it's enforced, it shouldn't be, I wish the code was clearer on this because it has always been and I guess will always be an issue.

    For me I try and keep it separated as much as possible. But as "much as possible" depends on how much money it will cost me and how likely I think I will be caught LOL
  • EdwinD
    EdwinD Member Posts: 159
    JUGHNE said:

    If you are doing some type of flex, I have found it simpler to mount a 4" square box on the boiler jacket and send a single flex to each device. Some controls have only a single knockout and room for 2 wires.
    I use 3/8" flex conduit and run the 14 GA stranded wire inside and loop thru the J-box up to the next control, etc. Fewer splices make for easier wiring and troubleshooting.

    @JUGHNE Question:

    If I run a single flex from the J-box to each device, how would this work in a series? I like your idea, just not sure how to do it.
    I was planing on running a series in the following order

    1) J-Box
    to
    2) Probe LWCO
    to
    3) Vaportstat
    to
    4) Pressuretrol
    to
    5) J-box

    1) Connect the hot (red) from transformer to BX-cable red conductor
    2) route BX cable and connect hot wire to 1st terminal in probe LWCO,
    3) next connect a separate BX cable hot wire to 2nd terminal probe LWCO and route to 1st terminal on Vaportstat,
    4) then hot wire 2nd terminal of Vaporstat then route and connect to first terminal of Pressuretrol
    5) lastly connect neutral wire to 2nd terminal of Pressuretrol, then connect to neutral wire (white) in J-Box.

    Is this correct ? Is there an easier way?

    The old LWCO is being taken out.

    See attached: flex cable, transformer for 24 volt wiring, and existing wiring for existing (old) pressure device.













    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • EdwinD
    EdwinD Member Posts: 159

    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • EdwinD
    EdwinD Member Posts: 159
    Weil-McLain EG55 2 pipe Vapor System
    OP Pressure .10 -.25 oz
    8-Way Boiler Water Treatment
    Barnes & Jones Big Mouth Vents
  • hot_rod
    hot_rod Member Posts: 23,393
    why not just low voltage wire, like 16 ga plenum wire? Stranded copper with aluminum jacket and plastic coat? Does 24V need to be in any conduit?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    EdwinD