One of my other hats that I wear
I found the entire bank of 13 lights out on the left field line. The butt splice connecting 2/0 al to #2 cu had burnt up along with the manual disconnect switch to which it was connected. For those not familiars with these larger crimp connectors: you can't use a wire size (#2 cu) that's three sizes smaller than the connector (2/0). It's a wonder it lasted 15 years with the amount of current these lights pull.
You can choose to do what you want, but you cannot choose the consequences.
Comments
-
Hey there, Bob:
I've seen that happen on aluminum wire before where the connection loosened and the aluminum wire started to arc.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
Agreed, but not readily available from our local supply houses. So, I used the splice blocks. I've got the hydraulic press tool, but they only stock butt connectors.JUGHNE said:I would use the H-type crimp. Blackburn WR series will do just about any combo in those sizes. IIRC the WR 289 with the "O" die does that connection. Fairly compact and easy to tape up.
Now Dominion Power... they have all kinds of goodies.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Alan, I've seen it more times than I can remember. To my knowledge, I've never had one of mine do it, but I'm very careful to do it "by the book". When you cut corners, this is the result. Aluminum wire is just not forgiving at all.Hey there, Bob:
I've seen that happen on aluminum wire before where the connection loosened and the aluminum wire started to arc.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Your fuse blocks look stressed. How far from the fuse block are the AL-CU transitions?0
-
The burnt one was replaced with the new one in the last pic.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Now you've made me feel bad. I just ordered some WR 289's online. I'll use them on the next pole as I'm sure it was done the same way.JUGHNE said:I would use the H-type crimp. Blackburn WR series will do just about any combo in those sizes. IIRC the WR 289 with the "O" die does that connection. Fairly compact and easy to tape up.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
-
-
I've been using the WR series connectors for the last 10 years with zero issues. I have a hydraulic crimper, and I really want a cordless crimper like the linemen keeping flaunting in my face. I just don't do enough to justify it. Although I have a ratcheting cable cutter that turns the linemen green with envy.0
-
It's the same with me Harvey. I've the Burndy MD68 hand crimper and a hydraulic one that goes up to 750m, but I just don't use them enough to justify buying a cordless... unless the right deal comes along.Harvey Ramer said:I've been using the WR series connectors for the last 10 years with zero issues. I have a hydraulic crimper, and I really want a cordless crimper like the linemen keeping flaunting in my face. I just don't do enough to justify it. Although I have a ratcheting cable cutter that turns the linemen green with envy.
I've been kinda hoping someone would come out with a crimper head that would connect to my ProPress.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I'm not sure if greenlee might have something? Seems I recall seeing something like that at a trade show.Ironman said:
It's the same with me Harvey. I've the Burndy MD68 hand crimper and a hydraulic one that goes up to 750m, but I just don't use them enough to justify buying a cordless... unless the right deal comes along.Harvey Ramer said:I've been using the WR series connectors for the last 10 years with zero issues. I have a hydraulic crimper, and I really want a cordless crimper like the linemen keeping flaunting in my face. I just don't do enough to justify it. Although I have a ratcheting cable cutter that turns the linemen green with envy.
I've been kinda hoping someone would come out with a crimper head that would connect to my ProPress.0 -
I did the right field line pole today. It hadn't burnt up at the splices yet, but "an ounce of prevention is worth a pound of cure".
Here are the old splices:
And here are the new including a new fuse block:
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Is that copper to aluminum? That might explain the failure of the splices.0
-
It is, but the failure of the butt splices was that the #2 cu wire was three sizes too small for the connector. That's why the connector is deformed.Harvey Ramer said:Is that copper to aluminum? That might explain the failure of the splices.
The H tap connectors that I used are rated for cu./al.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Gotcha0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements