Want to Replace Honeywell R8182D with three wire system
rickthebuckeye
Member Posts: 3
in Oil Heating
I have an old R8182D oil control aquastat. I would like to put in a smart thermostat, but my current set up has only two wires. What control/aquastat do I replace my old one with? And can I do it myself?
Rick
Rick
0
Comments
-
If by "smart" you mean Wi-Fi or internet aware, you are going to need the third, common wire. Those things suck power. You need to check if your system is 24 volt, and if it is use a common feed from the 24 volt transformer to the thermostat.
If, on the other hand, you mean programmable, there are a number of battery powered programmables -- I like the Honeywell VisionPro series, but there are other just as good (and some not so good...) which will do the job on two wires.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you. Yes I mean a WiFi enabled thermostat. I know about the third wire, and I'm not sure about the 24V on my current system. If I could just tap into the 24V (if that's what it is) that would be awesome.
I guess I need to figure out if the transformer in the control box is 24V and if I can tap into it. Any suggestions?0 -
Get a separate 24v transformer.
There was an error rendering this rich post.
0 -
Any suggestions where to get one and where do I mount it?0
-
I found one at a local home center once. In that case I mounted it on a wall and fed it with an inverter to keep the heat on in mid-winter extended power outage. You would mount in a standard electrical box and feed from utility/circuit.0
-
Is there air conditioning being wired into the wifi stat? If so, it might have an extra wire for a Common, or maybe run a new thermostat wire from the air handler.
If I remember right, the R8182D is a triple aquastat/primary?
If the above can't be done, you can install a 1 zone switching relay.(Taco, Argo etc.) Either offers a Common connection. This will need 3 conductors. Do you have an extra wire to use? Bring the thermostat wire and circulator wires to the new zone relay. Run a 2 wire from TT in the aquastat to N.O. dry contacts on the zone relay.
I dont know if Honeywell still makes the R8182D. Even remanufactured might be $$$.
If you can, install a new triple aquastat and a 15 sec primary control.1 -
Simplest way would be to use a Honeywell R8285B (DPDT) or R8239A (SPDT) fan center relay, which has its own 40 VA transformer. This mounts on a standard 1900 box (4" square). You'd power your thermostat from the transformer's R and C terminals, and connect the switched (usually white) wire to terminal G which operates the relay. Then you'd wire the normally-open relay contact to TT on the R8182D.
Does your boiler have a tankless coil to heat your hot faucet water?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
1 800 - call a pro0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements