A boiler that is too small

Can a boiler which just meets your heat loss be too small to use an indirect water heater? Indirect WH seem to rely on significant amounts of boiler to do the job. If you are at design outside temperature, do you have to make a choice between hot showers or warm house. Is there some point were a standalone water heater is necessary and what is the effect on overall energy use. Oil is my fuel of choice if that matters, no gas.

Comments

  • ScottSecor
    ScottSecor Member Posts: 896
    In certain circumstances the dhw load is,significantly higher than the heat loss. In those instances we may be forced to upsize the boiler and the indirect tank.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,559
    Pretty rare, usually a small house with large DHW loads or a big house with even bigger DHW demand :)
    To learn more about this professional, click here to visit their ad in Find A Contractor.
    kcoppSuperTech
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,559
    What is your heat loss and DHW requirement?
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Jon_blaney
    Jon_blaney Member Posts: 324
    I need about 55 MBH. I was looking at a BIASI B-10/3 which is rated at 61MBH, 53 MBH net. There is only two of us in the house now but want to be able to cover the needs when we have guests.
  • GroundUp
    GroundUp Member Posts: 2,076
    Can you set the DHW as priority? We've done this a few times in radiant floor applications with large thermal mass where the indirect pulling heat for an hour during high DHW loads has little effect on the heating comfort
  • jumper
    jumper Member Posts: 2,384
    Storage? Enough height for thermo-siphon?
  • Steamhead
    Steamhead Member Posts: 17,330
    GroundUp said:

    Can you set the DHW as priority? We've done this a few times in radiant floor applications with large thermal mass where the indirect pulling heat for an hour during high DHW loads has little effect on the heating comfort

    That's what I'd do, if boiler capacity is an issue. But, most times it isn't.

    The Biasi is a nice boiler. if it's installed and maintained properly, you should be happy with it.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    New England SteamWorks
  • Jon_blaney
    Jon_blaney Member Posts: 324
    I am going to connect it to two hydroair units. I will not have that thermal mass to keep us warm.
  • Then go with a stand-alone water heater, either storage or on-demand.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    edited April 2018
    I'm heating my home with an 50 K Munchkin , and it does DHW (output = 35K btuH, @ 5,280' ASL) on a limited priority, never had a problem. Only one person at a time can shower, but theres only 2 of us here anyway.

    ME

    There was an error rendering this rich post.

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,559
    What kind of DHW load?
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Leonard
    Leonard Member Posts: 903
    edited April 2018
    I've got a tankless coil in old CI boiler, I usually get all the steamy hot water I want for showers even when weather is a little cold.

    Few months ago when was a rare minus10 deg (about coldest it ever gets here) shower wasn't as hot as I wanted it. So I just set room thermostat down a few degrees to shut off room heating while I showered. Got 100% of boiler output for nice steamy shower. Nudged thermostat back up after, no problem. But have forced hot water cast iron baseboards, they cool slowly. And even at -10 boiler only ran 1 hr on & 1hr off for heating, 1.1GPH nossel.
  • hydro_newbie
    hydro_newbie Member Posts: 37
    @Jon_blaney it might be worth trying to get an idea of how quickly the house temp would drop if you were at design day and had no heat output. Although your system may not have a lot of thermal mass, your house will still have some.

    You can also get an idea of how much time it would take for the boiler output to bring the indirect back up to temp based on the amount of water used and your boiler's output. Idronics #17 (around page 15) has some info that might be helpful.

    @Robert O'Brien has asked about the DHW load. Some more info (family size, long showers, hot tub?) would give folks a chance to provide better info.
    ScottSecor
  • Gordy
    Gordy Member Posts: 9,546
    edited April 2018
    Look at it this way a 40 gal. conventional gas water heater is around 35-38k. Turning up storage temp, and using a mixing valve increases capacity. A mixing valve should be used regardless.
  • hot_rod
    hot_rod Member Posts: 23,127
    If there is such a thing as average DHW consumption, one rule of thumb is 20 gallons per day per person, or 20 for the first, 15 per each additional person.

    But it really depends on YOUR DHW wants and needs. A 50 gallon tank, running at 140F and a mix valve should work fine with that sized boiler.
    If you are an "average' DHW user :)

    Homes with hi-flow dual shower heads or large soaking tubs would be an exception perhaps.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    kcoppRobert O'Brien
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    And don't forget to cover the largest "dump" load, otherwise your wife may be unhappy in a partially filled soaking tub,,,

    ME

    There was an error rendering this rich post.

    GordyRobert O'Brien
  • Gordy
    Gordy Member Posts: 9,546
    Must keep wifey happy :)
    ratio
  • jumper
    jumper Member Posts: 2,384

    And don't forget to cover the largest "dump" load, otherwise your wife may be unhappy in a partially filled soaking tub,,,

    ME

    which is why you need enough storage OR REALLY POWERFUL heater. Latter has issues which is why tankless is not ideal for houses.
    Robert O'Brien
  • We have the same setup as Mark Eatherton; 50K Munchkin that heats the house (accelerator plates screwed to the subfloor) and a 50 gallon indirect, although we are low fliers; only 200 feet above sea level.
    When we have stay-over guests, I have to start thinking about DHW usage and let everyone know there is a limited amount available although we only have one bathroom and by the time a person has finished showering and left the bathroom, the water heater has recharged and is ready for another shower.
    Our design day is 36°, so DHW priority is not a huge problem; the indoor temperature only cools down a few degrees at peak DHW usage. If you're in a cooler climate, it will be more noticeable.
    Two types of people: those that will not tolerate any interruption of heating or DHW and those that are willing to work around it or put up with a minor inconvenience. If you're the former and don't want to be a guinea pig, get a separate, stand-alone water heater.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • kcopp
    kcopp Member Posts: 4,462
    edited April 2018
    I have a Buderus 115/3 Oil boiler. nets out @ 64 k btu. Installed autumn of 2003... Tekmar 260 control to prioritize HW.
    I have the heatloss for my home right on that line.
    Indirect WH is 60 gallon Superstor Ultra. 3/4" mixing valve on it. Tank set to 140.
    5 in the family. Including 3 teenagers w/ a daughter who loves her long shower...
    Never 1 time have I run out of hot water.
    Robert O'Brien
  • SuperTech
    SuperTech Member Posts: 2,387
    edited April 2018
    > @Leonard said:
    > I've got a tankless coil in old CI boiler, I usually get all the steamy hot water I want for showers even when weather is a little cold.
    >
    > Few months ago when was a rare minus10 deg (about coldest it ever gets here) shower wasn't as hot as I wanted it. So I just set room thermostat down a few degrees to shut off room heating while I showered. Got 100% of boiler output for nice steamy shower. Nudged thermostat back up after, no problem. But have forced hot water cast iron baseboards, they cool slowly. And even at -10 boiler only ran 1 hr on & 1hr off for heating, 1.1GPH nossle

    There's no way I could stomach (or afford, lol) keeping my boiler at 160 degrees 24/7/365. Tankless coils are a huge waste of fuel in my opinion. I prefer an indirect tank, but I'd rather have an electric water heater with a setback timer, or even a direct fired water heater over the thankless coil.

    But I really like your cast iron baseboards ;)
    kcopp
  • Leonard
    Leonard Member Posts: 903
    edited April 2018
    It's an old boiler. Dad installed it when he built the house some 60 years ago when oil was ~ 25cents /gallon. I do wonder if I installed a motorized exhaust damper if that would help with standby losses.