Radiant circulator size?
williamgxxx
Member Posts: 4
Would a taco 007 be adequate for a manifold with (2) 300’ loops in 1/2” pex?
0
Comments
-
Should be good.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
or maybe a small 3 speed circulator on speed 1. You are probably needing less that 1 GPM?lBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
That application is a challenge for most circs out there. It forces the circ to run very high on it's curve.
I like the Grundfos 15-58 a little better than the 007 for that application."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Domestic recirc pumps are an option, but usually more $$. I used this Grundfos UP 10-16 on a two loop system.
Or the B&G Vario dials down fairly low.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1