Are copper press fittings safe for Steam header?
bruce_21
Member Posts: 241
I visited my daughter-in-law's parents house over the holidays and they showed me the relatively new steam boiler in their basement. I was surprised to see a copper header made with press fittings. Will this work? I didn't say anything because I don't know if this works and didn't want to worry them
0
Comments
-
Propress fittings are rated for low pressure steam. I guess if you ask 10 people you will get 10 different answers.
Most on this forum (including me) probably don't think much of using them on a steam header but I don't want to speak for others they will chime in I am sure. If it was me it would be black pipe.
Time will tell how well it will hold up. Also, just noticed that the equalizer is taken off the header before the system take off which is incorrect. After both risers from the boiler hit the header the system steam supply is next followed by the equalizer.
Like many jobs we see that are not textbook it is possible it may work ok1 -
-
-
-
They live in a small town near Ithaca and said the R.E. agent that sold them the house told them there were only 2 or 3 steam systems in the town. This replacement job was likely done by the seller trying to save a few bucks when prepping the house. The puny many vents were probably there from before this boiler. I;m not sure where the pressuretrol could be piped on this boiler, maybe there are tappings behind the jacket that can't be seen in the picture.
0 -
Cleaver Brooks brought out a cast iron sectional that did not allow for all the low water cutoffs required for a system on guarded status. We had to get inventive with the trappings on the boiler to accommodate everything ,but we finally satisfied the Office of Mechanical Engineering. If you really look at the job and sit down with a pencil and paper you can satisfy the very nessicary safety requirements. In Manitoba ,any boiler in a public place ,has to be on guarded status if it is over fifty boiler horsepower. As for the vent, I stuck my head in a pipe chase on a main riser ,and that vent looks all to familiar to the one that was trying to be a main vent. I am also surprised at the connections for the pressuretrol, we have to pipe it on a manifold that is at least 3/4 inch and has crosses so all parts of the piping are open to inspection? I would also suggest that by the layer of concretions on the vent body it was ruined by water hammer the first or second cycle. I suppose ,at the risk of being a heating nerd ,why do we to attend trade school ,pass our government exams, and read constantly when this kind of work is allowed to exist? I am sad ,someone is going to be stuck with this kind of garbage. All the best Jack
0 -
Oh I just looked at the really nice professional way the suicide connector for the hot water tank is piped ,workmanship at it,s best? Tell your kids to hire a good tradesmen and get that mess repiped before someone gets hurt, good Lord!0
-
I just noticed the pigtail under the Pressuretrol is upside down also. It can't hold water and protect the Pressuretrol from steam that way.0
-
What is that piping material for the pressure relief valve, the drop to the floor?? plastic of some sort?0
-
That is what I thought, I have used them.
DHW T&P open at, IIRC 210F, but they are passing water under a good amount of pressure.
Steam could be well above 212 at 15PSI and have no water passing for "cooling" effect.0 -
Many things are wrong with that installation, but do you want to be the bearer of bad news? If you want to say anything, then start by saying the PRV should have a copper down tube on it, for safety.
Has it been working properly?—NBC0 -
i like how the header elbow reduces,thats a good restriction"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
Thanks for all your help! Pointed out a lot of things I hadn't noticed in the few minutes I spent in the basement. Extra eyes are very helpful!
They have been there a two or three years now and never complained about any problems so I guess it is functioning for the moment. I'll be visiting again this summer and start fixing the easy stuff that doesn't require a day and a half or embarrass the daughter-in-law's parents too much.0 -
At least it has 2 LWCOs. The pigtail will still collect water but I prefer them mounted in the steam space.
1 pressure control on 1/4" fittings is ok. Multiple controls should be on a 3/4 header if connected on the same tapping
@Jackmartin , what is guarded status?? Here in Massachusetts a manual reset LWCO and manual reset pressure control (for steam) or aquastat (for hot water) is required on anything larger than 200,000btu/hr.
I am assuming this is something similar0 -
well, here would be the best answer i can give to you...
''It will work for awhile''gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 855 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements