Installed new thermostat in 3 zone system, now weird things...?

Bgkob
Bgkob Member Posts: 2
Installed new thermostat on the lowest level of the Tri-zone boiler system (home is a Tri-level, lowest level has under the floor pipes, other levels are baseboard). About 4 days later the pilot light has been flickering and hot water will just, seemingly out of nowhere, stop flowing to the radiant baseboards and floor heating (lower), but the pilot light is still on...? I then switch the boiler off, wait 5 mins, switch back on and hot water comes back. Then soon the pilot light (flame or thermocouple..?) starts to click and flicker again. Repeat...

So is it an issue with my boiler? Or the new (very basic Honeywell digital screen type, like $20) thermostat?

Comments

  • Bgkob
    Bgkob Member Posts: 2
    https://youtu.be/wJ0eLGUDK7A

    Here is a 1 minute video of me showing the flick and click happening at the boiler. Ignore me attempting to sound like I know what I am talking about...because I don’t. :smiley:
  • Jamie Hall
    Jamie Hall Member Posts: 24,872
    Is this the pilot flame that is flickering? Gas boiler? You say the pilot light is still on, but is it on with a good solid flame?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Cross the thermostat wires several times, and see if the boiler fires. If it does, then try putting back the original thermostat, and see if it still works properly.—NBC
  • MikeJ
    MikeJ Member Posts: 103
    agree with nicholas jump out the stat and see if the problem goes away.