Added radiant heat loop to an existing hot water baseboard heat
rstryker
Member Posts: 1
We have a 25 year old Weil Mclain Gold GV boiler with 5 zones of baseboard heat. 2 years ago we put on an addition and added radiant heating as an additional zone to our existing boiler. It wasn't installed right and we are trying to get it to work properly. We have a contractor say we need to have a primary and secondary loops to our system with the existing 5 zones on one loop and the new radiant heat on another loop. Another contractor said we don't need it. Please advise.
Your radiant zone needs a mixing valve to reduce the water temp to the radiant zone. Tell us about the radiant installation type.
Suspended tube.?
Staple up with, or with out heat transfer plates?
Sandwich over the top method?
Gypcrete?
In all cases joist cavity insulation?
How are zones controlled? Zone valves? Pumps?
Primary secondary piping at the boiler is the way to go, or a hydraulic separator.
It also needs to have its own thermostat and circulator.Bob Boan
Adding pri/sec piping is not a bad idea but I believe it may be overkill for your project. It depends upon the size of the radiant. His concern is cold water coming back to the boiler from the radiant and therfore protecting the boiler. However, the amount of baseboard you have overshadows the size of the radiant, it will be hard to "shock" the boiler.
Take a look at the piping arrangement and make sure it looks like the attached. Radiant will need its own mixing valve and its own circulator as well as its own thermostat.
Dave H.
Dave Holdorf
Taco, Inc
Most GV boilers have a mixing valve or device under the hood to assure boiler protection, need more details to get you some options. The type of radiant installation and the BTU load would be helpful. As well as a pic of the current piping.Bob "hot rod" Rohr
Living the hydronic dream1 -
Pipe it as a branch off the return with its own pump and a 3way valve. That way it gets water that’s already tempered. Can drop your return temps and get more cooler efficiency that way... if using a mod con.
Ideally loads should be piped series parallel so DHW first, then fan coils or cast iron radiant then low temp radiant.0