Added radiant heat loop to an existing hot water baseboard heat
rstryker
Member Posts: 1
We have a 25 year old Weil Mclain Gold GV boiler with 5 zones of baseboard heat. 2 years ago we put on an addition and added radiant heating as an additional zone to our existing boiler. It wasn't installed right and we are trying to get it to work properly. We have a contractor say we need to have a primary and secondary loops to our system with the existing 5 zones on one loop and the new radiant heat on another loop. Another contractor said we don't need it. Please advise.
0
Comments
-
Your radiant zone needs a mixing valve to reduce the water temp to the radiant zone. Tell us about the radiant installation type.
Suspended tube.?
Staple up with, or with out heat transfer plates?
Sandwich over the top method?
Gypcrete?
In all cases joist cavity insulation?
How are zones controlled? Zone valves? Pumps?
Primary secondary piping at the boiler is the way to go, or a hydraulic separator.
0 -
It also needs to have its own thermostat and circulator.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Adding pri/sec piping is not a bad idea but I believe it may be overkill for your project. It depends upon the size of the radiant. His concern is cold water coming back to the boiler from the radiant and therfore protecting the boiler. However, the amount of baseboard you have overshadows the size of the radiant, it will be hard to "shock" the boiler.
Take a look at the piping arrangement and make sure it looks like the attached. Radiant will need its own mixing valve and its own circulator as well as its own thermostat.
Dave H.
Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -
Most GV boilers have a mixing valve or device under the hood to assure boiler protection, need more details to get you some options. The type of radiant installation and the BTU load would be helpful. As well as a pic of the current piping.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Pipe it as a branch off the return with its own pump and a 3way valve. That way it gets water that’s already tempered. Can drop your return temps and get more cooler efficiency that way... if using a mod con.
Ideally loads should be piped series parallel so DHW first, then fan coils or cast iron radiant then low temp radiant.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements