Vibrating/Humming Pipes via Taco Circulator Pump
Link to gallery:
https://imgur.com/a/Xznm7
I already purchased some anti-vibration rubber and tried to wedge it in all the places the pipes were touching. That seemed to help very little. Pulling the pipe going into the wall down with my hands reduces the noise some. I think I need to somehow clamp the pipe far more securely. Right now they are loose and you can shake them about. Perhaps I could cut my own vibration rubber into strips to attempt to line a hanger of some kind?
Obviously you are professionals and you'd recommend fixing the pump (Called Taco tech support; they recommended repair solutions) or doing all kinds of great things, but how can I try to help myself here? Management has refused to help, citing the pump is operating normally.
If you know any specific hangers or clamps that I can purchase easily, I'd greatly appreciate it. Thank you in advance!
Comments
-
If the pump is transmitting the humming through the pipes -- they are rigid copper? -- just clamping and isolating the pipes from everything else it may not help much.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Yes, they are rigid copper.Jamie Hall said:If the pump is transmitting the humming through the pipes -- they are rigid copper? -- just clamping and isolating the pipes from everything else it may not help much.
I was hopeful someone has been able to fix a similar problem. When I use Google to search all I can find are instructions for periodic banging pipes, not one ringing/humming 24/7.0 -
It may be pumping too fast. When my viridian revs up on the start cycle you can hear it hum in the pipes. But when it runs cycle you cannot hear it0
-
That's good to know. Unfortunately, the repairman that came out insisted the pump was functioning properly. Keep in mind, you could hear the pump vibrating off the wall and down the hallway a good 80 feet away. What he did was hammer a hole into the wall where the pump was touching and it reduced the noise around the pump. But it's still vibrating, of course, and thus the pipe hum is exactly the same in our unit. He didn't even check with me after to see if there was any change.Leon82 said:It may be pumping too fast. When my viridian revs up on the start cycle you can hear it hum in the pipes. But when it runs cycle you cannot hear it
It's a frustrating situation. Thus I'm on the internet asking you experts here for any solutions so my girlfriend and I can avoid breaking our lease and the expense of moving in the middle of winter.0 -
If it is pumping too fast -- which is quite possible -- it isn't because something is wrong with the pump (although it could be the wrong pump for the job), but rather something with the whole setup.
Usually when a noise or vibration is transmitted through a pipe, and one can't eliminate the source for one reason or another, the only solution is to install a flexible connection on the pipe which won't transmit the vibration. In a rental this may be hard to do...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
How long have you noticed the noise - or did it just start? Harmonics are sometimes extremely difficult to trace - how was it confirmed it's the circulator? Has someone turned it off and the noise stopped?
Sorry for the seemingly "stupid questions" but before we start replacing stuff it's good to zero in on the exact cause as much as possible...0 -
The electric flex going to that pump looks to have a solid coat of paint on it. Almost to the point of being steel pipe.
You might try flexing that to break some paint off and see if it changes anything. Just a long shot, but stranger things have happened.0 -
Could be you have more pump than you need also, how was the pump sized?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Hi Steve, thanks for your reply.Steve Thompson (Taco) said:How long have you noticed the noise - or did it just start? Harmonics are sometimes extremely difficult to trace - how was it confirmed it's the circulator? Has someone turned it off and the noise stopped?
Sorry for the seemingly "stupid questions" but before we start replacing stuff it's good to zero in on the exact cause as much as possible...
The noise is only present when the boiler and pump have been active. The heat was intermittent in early September, thus we were able to deduce it was related to that. Since the heat has been on in the building consistently, it is 24/7.
The noise is loudest directly at the spot the pipes enter into our apartment. The pipes run the length of the wall and subsequently so does the noise. It's a hum in the wall running along the exact spot the pipes would be.
The only thing we can perceive to be causing this hum is the circulator pump that is shaking very slightly, but enough to create resonance along the pipes. You can hear and feel the vibrations, albeit slight. The volume is comparable to a florescent light hum.
Ultimately the management company's repair crew has claimed this is not a problem (despite the fact our apartment hums) and so I'm searching for solutions I can find. More specifically, if I can dampen the vibrations with hangers or clamps that I can install on my own, since I have access to the pipes in the utility room.0 -
Sorry about this, but most rotating elements -- such as a pump -- vibrate very very slightly. If they are rigidly connected to something -- such as a pipe -- which can transmit the sound it will. And sometimes the only cure is a flexible connection.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Occasionally debris gets caught in the impeller and throws them out of balance, teflon tape, copper or steel pipe shavings, rust particles, etc. You may need to remove the pump from the body and check the impeller.
The higher rpm type of circulators are more prone to telling you when they are out of balance.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
A vibration isolating pipe hanger might help a bit. I don't think it will fix the problem because the pipe is tight to drywall and probably framing where it goes through the wall.
The 0011 is a very robust circulator to be attached to 1" pipe. It is likely pushing more than twice the recommended (or needed) velocity. Your noise could be velocity or the groaning of circulator that is incorrect for the application."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
@WizardGygax
You can fix that issue, without determining the exact cause by adding mass to the piping system. Find some suitable steel bars and securely tape or rigidly strap them to the piping. You want to add about 10 lb. to the assembly. This will prevent the acceleration of the piping which is generating the noise.
Sure, you can probably install a smaller circulator at additional cost, but the additional mass will solve the current problem at minimal cost.
The final alternative, which does not look feasible, is to somehow secure the piping to something with tremendous mass (like the building).0 -
I suspected the same, looks like a lot of pump for the piping and boiler we see in the pic.Zman said:A vibration isolating pipe hanger might help a bit. I don't think it will fix the problem because the pipe is tight to drywall and probably framing where it goes through the wall.
The 0011 is a very robust circulator to be attached to 1" pipe. It is likely pushing more than twice the recommended (or needed) velocity. Your noise could be velocity or the groaning of circulator that is incorrect for the application.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I am going to go ahead and ,em, disagree with this.SeymourCates said:@WizardGygax
You can fix that issue, without determining the exact cause by adding mass to the piping system. Find some suitable steel bars and securely tape or rigidly strap them to the piping. You want to add about 10 lb. to the assembly. This will prevent the acceleration of the piping which is generating the noise.
Sure, you can probably install a smaller circulator at additional cost, but the additional mass will solve the current problem at minimal cost.
The final alternative, which does not look feasible, is to somehow secure the piping to something with tremendous mass (like the building).
Oversized circs eat pipes, waste energy, cost more and don't last very long.
If the OP installs a correctly sized ECM circ, the system will run quieter and cost less to run. Putting weights on it may make it quieter but is just plain silly and unprofessional. Strapping it to the building will just change the pitch of the noise."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Thank you for this recommendation. Can you describe specifically how I might affix the weight to the piping? Where I should be putting it? Near the pump? Running horizontal/vertical? My photos from the first post detail the piping setup.SeymourCates said:@WizardGygax
You can fix that issue, without determining the exact cause by adding mass to the piping system. Find some suitable steel bars and securely tape or rigidly strap them to the piping. You want to add about 10 lb. to the assembly. This will prevent the acceleration of the piping which is generating the noise.
Sure, you can probably install a smaller circulator at additional cost, but the additional mass will solve the current problem at minimal cost.
The final alternative, which does not look feasible, is to somehow secure the piping to something with tremendous mass (like the building).0 -
Unfortunately, the property company says everything is running great, so installing new equipment isn't an option. I agree I wish this was being handled more professionally.Zman said:
I am going to go ahead and ,em, disagree with this.SeymourCates said:@WizardGygax
You can fix that issue, without determining the exact cause by adding mass to the piping system. Find some suitable steel bars and securely tape or rigidly strap them to the piping. You want to add about 10 lb. to the assembly. This will prevent the acceleration of the piping which is generating the noise.
Sure, you can probably install a smaller circulator at additional cost, but the additional mass will solve the current problem at minimal cost.
The final alternative, which does not look feasible, is to somehow secure the piping to something with tremendous mass (like the building).
Oversized circs eat pipes, waste energy, cost more and don't last very long.
If the OP installs a correctly sized ECM circ, the system will run quieter and cost less to run. Putting weights on it may make it quieter but is just plain silly and unprofessional. Strapping it to the building will just change the pitch of the noise.
So I want it to run quieter even if it's silly and unprofessional! We just want to survive the winter by reducing the noise.0 -
Weight is not going to solve an out of balance circulator, or one that is running off it's curve.
It needs to be confirmed that it is sized properly, and removed and inspected. It should run virtually silent.
Any other fix is just a bandaid for a more serious problem, I suppose.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
How about this... I arrange to have a 0011 cartridge (the complete rotating assy including impeller) sent to your attention no charge. You get it to the maintenance folks for them to install (requires draining the pump). The part number is 0011-009RP. Or, we'll replace the complete circ no charge (although is likely oversized).
I can get you product, just can't get it installed for you.4 -
This is an extremely generous offer. I will attempt to pass it along to my management company. Thank you so much.Steve Thompson (Taco) said:How about this... I arrange to have a 0011 cartridge (the complete rotating assy including impeller) sent to your attention no charge. You get it to the maintenance folks for them to install (requires draining the pump). The part number is 0011-009RP. Or, we'll replace the complete circ no charge (although is likely oversized).
I can get you product, just can't get it installed for you.
Is there any information should I pass along to the maintenance guy regarding a possible oversized pump?0 -
We can offer a ECM self sensing circ of the same size that will slow down based on the flow and load demand but I don't want to be responsible for messing up the system that has been heating properly (I assume). For sure this would 100% eliminate the possibility of oversizing.
If the management company is concerned about setting this "smart" pump up we can hook them up with our local rep or they can contact me directly at (401) 441-2934.
I feel your pain about the noise - some might not see it as a big problem but clearly you want to get rid of it and it is bothering you. Solutions are there - just need to the way to "get er done".1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements