Taco sr503 relay question

Leon82
Leon82 Member Posts: 684
I'm only using zone 1 and 2 and the tt contact goes to the first tt input on the boiler.

I want to move the 2nd zone to the priority zone 3 and use the priority tt to the second tt input on the boiler to run a separate odr/temp curve. But I want the priority function inactive

I read the directions a few times and am a little confused. Do both end switch close when the priority zone calls for heat? If so it is going to kill my plan

Thanks

Comments

  • Dave H_2
    Dave H_2 Member Posts: 594
    It sounds like you have a SR503-EXP? Am i correct?

    The -EXP controllers have two separate end switches (XX). The "Main End Switch" only closes upon a heat call from any heating zone, in your case Zone 1 and Zone 2.

    The "Priority End Switch" only closes when Zone 3, the priority zone, is calling for heat as long as the priority switch is on.

    Dave H.

    Dave Holdorf

    Technical Training Manager - East

    Taco Comfort Solutions

    Leon82
  • Leon82
    Leon82 Member Posts: 684
    Yes , exp.
    Thanks
  • Leon82
    Leon82 Member Posts: 684
    edited November 2017
    It looks like it won't work like I had hoped.

    I'm getting 7 volts across rw on a the zones NOT calling for heat. Is this normal?

    It is a battery thermostat with only 2 wires
  • HVACNUT
    HVACNUT Member Posts: 6,475
    When the thermostat is open, it should read 24v across TT for that zone because it's kind of a false reading as it's picking up voltage through the relay coil.
    When the thermostat is closed, it should read 0v across TT
    Leon82Zman
  • Leon82
    Leon82 Member Posts: 684
    Ok, thanks. The one that's closed is at zero currently